Class I and CLass II | on ElectriciansForums
Discuss Class I and CLass II in the The Welcome Forum area at ElectriciansForums.net
leigh
I understand what Class I and Class II are i.e earth cable or double insulated, but is there anything which states when one should be used over the other or is it just a choice ?
one pointer is if you have a lighting circuit from the 1960's with no cpc. you'd then use only class II fittings.
Class II equipment either use double insulation or a single layer of reinforced insulation for basic protection. Accessories such as plastic light switches or batten holders are not considered to be double insulated.
use double insulated/class II if you have a free choice, especially outside the house, as it reduces the (already small) risk caused by having earthed metal around.
Interesting observation! Although the lampholder itself is marked with the double square (even though it has exposed contacts with the lamp removed) the rose itself has no such marking. Perhaps that's because it comes under a junction box standard rather than an appliance in some way?
Batten holders do not provide double insulation and yes I have seen the labels on them. Batten holders generally provide no provision for basic protection, see the Note at the end of Reg 416.2.4
Reply to Class I and CLass II in the The Welcome Forum area at ElectriciansForums.net
Thanks for your reply. You are quite right, I’ve taken one down this morning and the cable is twin & earth but the earth has been cut right back...
The manufacturer has stuck a label on the baseplate, its clear to see. I don't know what instructions came with the fitting or what was written on...
2 3