Hi all, carried out an EICR recently on a caravan. System is a TT with 4293 100ma main switch then into a 3036 board. All wiring tested ok with just a few damaged accessories to change. RCD tested ok but its not time delay. Should I be recommending additional 30ma RCD protection for circuits (in walls, bathroom and outside socket)?
 
Hi all, carried out an EICR recently on a caravan. System is a TT with 4293 100ma main switch then into a 3036 board. All wiring tested ok with just a few damaged accessories to change. RCD tested ok but its not time delay. Should I be recommending additional 30ma RCD protection for circuits (in walls, bathroom and outside socket)?
You should Code them appropriately. Is there supplementary bonding to the bathroom?
 
oops, misread OP. thing is, with a caravan, the site connection is usually on a 3omA RCD anyway. is this a static or a tourer?
 
No supplementary bonding which I have noted as C2. So I suppose that C2 would apply to absence of 30ma RCD protection too.
Maybe if the sockets are likely to supply equipment outside...I would say it's likely the case being a caravan. Then you also have to consider the installation method and what code it warrants.
 

Reply to Classification code for 100ma TT 3036 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
888
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top