N
novolts
Hi Guys I have been plucking up the courage to ask a couple of questions at the grand old age of 55 I am starting to do testing and inspection and maybe once I have asked my questions some may feel that my test instruments should be taken off me .I was carrying out a Periodic recently and the condition of the previous inspection was classed as satisfactory. The first thing I noticed was that a 20 amp circuit breaker was fitted at the main sub board however the circuit breaker did not fill the full cut out of the main sub board cover and it would not be hard to come into contact with the live conductor I would class this as a C2 The other potential risk I noticed was that there was a triple pole circuit breaker rated at 80 amps that fed a 3phase(line) isolator the isolator was fed with a 25mm SWA. The isolator was for a supply to a lift, the cable feeding the lift from the isolator was a 4 core 2.5 mm cable I did a load test on 1 of the phases if the lift as going from the 1st floor to the Gnd floor it drew 18amps however if it went from the Gnd floor to the 1st floor it drew 32 amps the lift is hydraulic I would also class this as a C2 sorry for the long thread but advice would be greatly appreciated novolts PS I am thinking that the quickest way to resolve the issue with the lift is to de rate if possible the size of the circuit breaker at the sub mains and install at least a 4core 6mm cable between the isolator and lift control panel