I would appreciate some opinions on the following situation...
I have been asked to comment on an EICR for a local community resource (church hall used by various groups of all ages).
During an EICR on the TN-C-S installation the testing of a ring final circuit gave R1+R2 and Zs(db) values that when added together exceeded the maximum acceptable for the MCB type and current rating. This would imply the RCD was required for fault protection.
When Zs measurements were made around the ring the maximum measured Zs value was found to be lower than the required value for satisfactory fault protection by the MCB. This would imply the RCD was present only for additional protection.
I assume the Zs readings from around the ring are lower because of a fortuitous parallel earth path through a gas and/or water pipe. I consider this an earth path, however it comes about, to be one that cannot be relied upon as it is not part of the electrical installation and could change (eg a metal pipe could be replaced by plastic) so my inclination is that the RCD as necessary for fault protection. The EICR records it as for additional protection only.
Opinions on this?
I have been asked to comment on an EICR for a local community resource (church hall used by various groups of all ages).
During an EICR on the TN-C-S installation the testing of a ring final circuit gave R1+R2 and Zs(db) values that when added together exceeded the maximum acceptable for the MCB type and current rating. This would imply the RCD was required for fault protection.
When Zs measurements were made around the ring the maximum measured Zs value was found to be lower than the required value for satisfactory fault protection by the MCB. This would imply the RCD was present only for additional protection.
I assume the Zs readings from around the ring are lower because of a fortuitous parallel earth path through a gas and/or water pipe. I consider this an earth path, however it comes about, to be one that cannot be relied upon as it is not part of the electrical installation and could change (eg a metal pipe could be replaced by plastic) so my inclination is that the RCD as necessary for fault protection. The EICR records it as for additional protection only.
Opinions on this?