Dkeano76

Hey all, just wondering if any can can give me some info regarding clean/dual earth. It's in a school computer room in dado trunking. Have an idea to what it is but not sure about terminating of it or what size 2nd earth (if that's the case) should be.
Cheers.
 
Hey all, just wondering if any can can give me some info regarding clean/dual earth. It's in a school computer room in dado trunking. Have an idea to what it is but not sure about terminating of it or what size 2nd earth (if that's the case) should be.
Cheers.
 
If the circuit is run as a ring then will be fine but twin earth terminal sockets have to be used with one leg in each, also each leg of cpc at the board must be terminated separately and not put together. the idea being that computer circuits dump current to earth so if an earth becomes detached it will still have a remaining earth parth, hence the separation of terminals.
the circuit can also be run as a radial but a second earth has to be run forming a ring on the cpc as it were. must admit IMO i prefere the ring method, as i'm not a lover of radials but if this is for a school its normally scheduled for you, have you checked ?
 
As Phil says, you should have spares.
Its also good practice to label the board with possible high earth currents blah, blah but importantly to label the cpc's of that circuit as the terminal numbers will not match for identification later by someone else.
 
I'd prefer to install a second earthing terminal, marked up to show which circuits the cpc's belong to than to share another circuits terminal.
That way you can maintain circuit order and not have it listed as a defect when am EICR is carried out.
 

Reply to Clean/Dual Earth in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

I tend to write the circuit number on the mcb say every 5th mcb/rcbo just to help make it easier to locate in a large multi way or 3ph board...
2
Replies
17
Views
889
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top