Hi,
I have been asked to provide a "clean supply" for a new fire panel installation. What does the phrase "clean supply" mean to you guys. A clean earth - if so, how would you deliver this? Something different?????

Serious question, serious answers please!:p

Thanks,
George
 
It is basically an earth which as no noise on it ...................so clean and therefore no interference.

In this case I would imagine they will want you run a seperate circuit from the CU to the panel. Is this an actual Spec as the "clean Earth" term is mostly associated with older IT equipment and with modern day technology is not that critical. Is this an old panel?
 
Thanx Malcolm. A verbal rather than written spec for a new fire alarm panel. So in your eyes, a new radial circuit supplying only the FP. I'm guessing the guy spec'ing the new supply has picked up the terminology from somewhere, but I wanted to check my understanding before getting back to him. Does the cpc in a clean earth supply require to be a minimum size, or terminated in a special way?

George
 
Normally all that was done 15-20 years ago when computers and VDU were being fitted was that each station was fed from it's own individual radial. so if you had 10 stations you had 10 radials feeding them .................often in large offices you would see a sub board which these radial terminated into but, the CPC for that board still terminated back via however to the MET.

It was felt that by using individual circuits you cut down on the noise becasue you only had the one individual item of equipment on a circuit and so no interference. But as said most modern equipment have filters and that brings it's own joys .
 

Reply to Clean supply? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
705

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
699
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top