Hi all
Wondered if you could clear up a debate we are having at work.
Gas inspection has said no bonding to the gas meter or pipe in block of flats.

One engineer says it should be run to the meter.
One says it should be installed outside within 600mm of where it enters the building on the blue arrow.
And one engineer says it should be inside 600mm from where it enters the flat.
What do you all think.
[ElectriciansForums.net] Clear up a bonding debate of ours.
 
BS7671 states, where practical the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external.
So, I would suggest your last engineer is correct.
 
DNO policy document for multi way distribution systems (Ryefields) requires bond at the incomer plus a bond in each individual flat
 
BS7671 states, where practical the connection shall be made within 600mm of the meter outlet union or at the point of entry to the building if the meter is external.
So, I would suggest your last engineer is correct.
You would have to say internal.
 

Reply to Clear up a bonding debate of ours. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
600
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
706
loz2754
L
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top