hi guys

just wondering if anyone knows current best practice for running cables in plastered chases?

i have always clipped direct to wall and capped , but on reading some past posts many seem to use either 20mm conduit or oval tubing and class clipping to the wall as a DIY approach. i like the idea of using a conduit or tube (easier to install or remove cable) but surely it would change the ref method and derate the cable? or is this disregarded due to being a short run, that said a socket to a ceiling could be over 2m.

many thanks
 
if using oval tube, i would not derate the cable. it's only like having capping under and over, but easier to replace cable if ever required.
 
Clipping to wall is fine. I do this if dot and dabbed. Only cap if to be plastered onto as this is (99% of time) cappings use-to stop plasterers trowel damaging cable.

Oval tubing is a dream to find if rewiring and i should start doing it more often!
 
i see your point telectrix, just when reading OSG caping/conduit enclosed in a wall would be ref meth b. which for 1.5mm lighting circuits would be fine, but for a ring main circuit 2.5mm would be right on the limit. so i guess its like you say it depends on which ref method you use .
 
Personally I always use oval, slide it on, put the bow toward the wall, clip in the top, clip in the bottom and ready for the spread. It's then easier to sort for me or the next guy when the builders or the customer puts a nail in it. And it looks a million times better (yea I know it's going to be covered over but come on, let's have a bit of pride in our work). I used to be an advocate of top hat, but as soon as I used oval I was hooked.
 
Clipped direct is sound mate, whoever said its DIY approach needs to look at the regs. Aslong as your RCD protected capping is fine.
 
does anyone know how the regs class oval tube/conduit with regards to cables in chases.
as id like to use an oval tube but logic tells me that you would have to derate if you enclose in tube or conduit, is it classed as a protective measure like capping ??
 
Derating? Come on, the only standard circuit that is realistically likely to be affected by the derating factor in oval is a shower circuit with a (240v) 9.5kW on 6 mil, and if that bothers you (it wouldn't bother me, it's in a wall not on a wall) then wire it in singles in conduit in or on a wall and there we are. If we are going to be worried about the derating factor of buried oval, we should be worried about top hat capping as well - the cable is not completely enclosed in plaster - there is a small void and one PVC surface, both of which will insulate and stop the dissipation of heat that you would get in purely buried plaster. It's all a load of tosh, and in real terms I doubt you would lose an eighth of an amp in top and maybe a quarter of an amp in oval buried in the wall, and on a shower, which is only going to be used at 10 minutes at a time and only at half-mast when it's hot outside, I don't think that amounts to a whole hill of beans.
 
Crampets? What do you call crampets? I call them these spikey mo-fos you strap to your feet to climb poles, what do you call them? Or was that crampons\? Ahh beer, once again you foil my plans to think proper.
 
Crampets? What do you call crampets? I call them these spikey mo-fos you strap to your feet to climb poles, what do you call them? Or was that crampons\? Ahh beer, once again you foil my plans to think proper.

Thats Crampons!, what would you be doing up a mountain anyhow.

Crampets!!, same price as pvc oval clips but half the time to beat them into the wall. Just look a bit pony! but as they are in chases, it matters not a jot!

crampets~5342.jpg
 
Last edited:
those for climbing poles arnt crampons, they have the spikes on the side, my grandfather who was a Forrester in northern Ireland used to use them!!, crampons are for mountain climbing

Mind you what the hell are u doing up telegraph poles?? u fiddeling your phone bill again?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
clipped cable in chase
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
ianphilip007,
Last reply from
High Tower,
Replies
28
Views
10,542

Advert

Back
Top