Hi,
I have had PIR done on a flat that was built in 1991, I have had a code 2 on the lights in the bathroom not on an RCD even though it is an IP 56 fitting, is this correct? The maximum demand has also been put at 50KVA for a 2 bed flat...!

Thanks
 
code 4 for the bathroom lights, as long as there is no apparent danger. 50kVA is probably he meant 50A.
 
Has there been any alterations to your bathroom lights ?

If not and supplementary bonding was in palce and tested OK IMO I would not code it !
 
The ESC guidance (which I do not agree with), is no code at all.
I'd go with a code 4 as well.
 
Last edited by a moderator:
The bathroom should have either RCD protection on all circuits or supplementary bonding.

If SB is in place then lack of RCD = code 4

If no SB in place there should be two coded items:
No SB = code 2
No RCD = code 2

IMO

Has the supp bond box been ticked on the schedule?
 
FFSFFS 16th edition its no code but a N/A note as not compliant with CURRENT regs but compliant when originaly done
 
ive allways worked on the idea of a pir/eicr is to evaluate the installation against the CURRENT version of the regs, if the install was to an earlier version of the regs then issues such as above would be a code 4 but now what would they be a C3 or no code??
 
Last edited by a moderator:
Tho don't but they weren't happy with our coding and informed us that is how they want it done!!
 
I have no idea what they didn't like about your coding, maybe they had cause and maybe not!! But they can't and/or shouldn't be telling you how THEY want it done!! You follow the national guidelines laid out in the relevant authorities, which i guess would be the IET in this case...
 
Just to put a spanner in the works.
Whilst the IET along with the BSI, has the responsibillity for conceiving, formulating, writing and publishing the Regulations.
In actual fact, the NICEIC, along with representatives of just about every other electrical organisation provide members of the comitee that does the work.
So technically the NICEIC do write the Regulations, or make the rules.
 
Just to put a spanner in the works.
Whilst the IET along with the BSI, has the responsibillity for conceiving, formulating, writing and publishing the Regulations.
In actual fact, the NICEIC, along with representatives of just about every other electrical organisation provide members of the comitee that does the work.
So technically the NICEIC do write the Regulations, or make the rules.

If that's the case, ...they shouldn't start trying to change them, or put there own tilt on what's been stated and approved for publication by the controlling committee... They can wait and put forward there ideas at the next committee meeting, for them to be accepted or otherwise. ..lol!!


They are only a representative part of the committee that make or set the Reg's or rules, so technically they on there own don't actually make any rules. Not that you would see that, in the way they try and make there own rules up, in some of the publications that i've seen...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

UKMeterman

Arms
-
Joined
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Code 2 for non RCD lights in a bathroom
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
UKMeterman,
Last reply from
Engineer54,
Replies
15
Views
8,365

Advert

Back
Top