I would agree with Tel on the C3, it is borderline no code.
Generally heavy consistent loads should not be placed on a ring final because of the potential to overload one leg of the ring. However an oven is not a consistent load, although 18A is fairly heavy for a single point on a ring, with 4mm² conductors one leg of the ring cannot be overloaded even with a type 2/type C hydraulic MCB @ 30A.
Assuming all other factors remain compliant I cannot see it giving rise to danger but I can see it possibly tripping the circuit breaker but no more than with any socket circuit really as there are only four (six) points of use, unless the general use sockets are often used for heating loads by the nature of the installation.
I am probably pushing the justification for a C3 but feel that even an 18A oven should be on its own circuit so would recommend improvement from a design rather than a danger point of view.