Hi guys, I am doing some repairs on a big night club job we tested a few months back and the customer is arguing a few of my faults:

1. All the earths at the downlights have been cut away, they are plastic downlights but surely it is still potentially dangerous if the earth doesn't exist ie.. Change to chrome fitting etc..... I marked this is a code 2, am I right or wrong??

2. One of my colleagues has marked a d/b fed directly from a busbar (no isolation) as a C2, I was thinking C3?

3. No metal trunking lid with singles running through it, above head height C2 or C3?

4. And now for a off topic question I was at a house yesterday to fix a socket and customer complained about flickering lights, after further investigation i noticed the neutrals were slack in joint box, problem fixed!!! But prior to finding the joint box I tried testing voltage at a light switch between L-E using a fluke volts tester and everytime this would trip the RCD, is this related to the slack neutral connections ?



Again thanks in advance
 
Hi guys, I am doing some repairs on a big night club job we tested a few months back and the customer is arguing a few of my faults:

1. All the earths at the downlights have been cut away, they are plastic downlights but surely it is still potentially dangerous if the earth doesn't exist ie.. Change to chrome fitting etc..... I marked this is a code 2, am I right or wrong??

2. One of my colleagues has marked a d/b fed directly from a busbar (no isolation) as a C2, I was thinking C3?

3. No metal trunking lid with singles running through it, above head height C2 or C3?

4. And now for a off topic question I was at a house yesterday to fix a socket and customer complained about flickering lights, after further investigation i noticed the neutrals were slack in joint box, problem fixed!!! But prior to finding the joint box I tried testing voltage at a light switch between L-E using a fluke volts tester and everytime this would trip the RCD, is this related to the slack neutral connections ?



Again thanks in advance

1)I wouldn't say code 2, the fittings dont require an earth, in future the wiring would have to be altered if they wanted chrome fittings but at the moment it's not potentially dangerous.

2)I wouldn't say that was a code 2 or a 3.

3)Think I'd go for a C3
 
Cant really disagree with either of the above re the codes, as ong as the findings are backed up with specific regs its not an issue. The RCD may have tripped as certain fluke voltage testers will trip the RCD. I cant remember exactly why, but I remember it being discussed in college.
 
If the earths are cut off, there will be no continuity of CPC along the cable (I'm assuming T+E). That's a no no!!
 
1) No code, or at most Code C3. Whilst the Regulations now require in the 17th edition for a CPC to be run and terminated at every wiring point and accessory, in this particular instance there appears to be nowhere to terminate the CPC.
Yes running a CPC is good practice, but can you really apply a code because someone in the future might do something that doesn't comply?
2) No code for feeding the second DB from the first. Code C2 if there is no main isolator for the installation.
3) Code C2. Non-sheathed cables should be in containment. Whereas in the 16th IP3X was allowed, it now has to be IP4X or IPXXD.
 
Hi guys, I am doing some repairs on a big night club job we tested a few months back and the customer is arguing a few of my faults:

1. All the earths at the downlights have been cut away, they are plastic downlights but surely it is still potentially dangerous if the earth doesn't exist ie.. Change to chrome fitting etc..... I marked this is a code 2, am I right or wrong??

IMO regardless of whether the cpcs are connected to the actual downlights, I would suggest they were at least connected through the entire circuit length for continuity and the fact a metal switch may be evident somewhere, a requires improvement for me there, hard hat on hehe
 
I don't think that the OP is stating that there is no CPC run to the switch, just that the CPC has been cut at each down light.
We are required during a periodic inspection, to note any damage, deterioration, defects, dangerous conditions and non-compliance with the Regulations, which may give rise to danger.
Has the CPC been damaged?
Has the CPC become defective?
Is the lack of a continuous CPC a dangerous condition?
Is the manner in which the CPC has been installed a non-compliance which may give rise to danger?
If you believe that the answer to any is 'yes', please explain why.
 
I actually foned a SELECT technical advisor today and he agreed with coding the downlights a code 2, 1 of the main issues he had was if the cable was to be accidentally screwed or vermin were to chew the cable the earth would be needed to trip RCD etc.... He basically said earth is needed to protect cable as well as appliance/fitting etc.... Thoughts?
 
I would suggest the cpc should be continuous. Otherwise, how do you test Zs?
Also, I'd say redundant cores in a multi core cable ideally want grounding down to earth.
Tin hat on!
 
It is not clear from the OP whether the cpc is continous. ie. is it just the cpc to the light fitting that is cut or all the cpcs on a loop in/out system. If the former I wouldn't code it. If the latter. i.e. you have a cpc but no continuity anywhere then I might be tempted to go with a C2 if any of the fittings have metal (switch screws for example) as they could be made live in a fault. If everything is class II and no earthed accessory screws then maybe a C3?

For 3) I might go for a C3 if I could convince myself that there was no chance of anyone touching it but generally I'd agree with a C2.

Just my own views... ;)

@tigerpaul If I find a lighting circuit with no cpc but all class II (quite common in houses of a certain age) then I test L-N loop impedance and record that instead of Zs (with a note of what I have done of course). Others might comment on this......
 
If the cable is accidentally screwed or chewed by vermin, there is no guarantee that both the line conductor and the CPC will be caught by the screw or vermin.
This is why, RCD protection is a method of providing additional protection for cables concealed in walls.
Are the downlights installed in walls by the way?
RCDs do not require a CPC to operate, if they did, then there would be no point in plugging your hedge trimmer into an RCD protected socket.
A CPC is not there to protect the cable.
It is there to earth exposed-conductive-parts which may become live under fault conditions, and to provide a path for earth faults which may occur in equipment conected to the wiring system.
 
It is there to earth exposed-conductive-parts which may become live under fault conditions, and to provide a path for earth faults which may occur in equipment conected to the wiring system.
Why does the CPC need continuity throughout the circuit?
If there's continuity to the parts and equipment that needs to be earthed, what is the danger if there is no continuity to other parts and equipment?
 
Why does the CPC need continuity throughout the circuit?
If there's continuity to the parts and equipment that needs to be earthed, what is the danger if there is no continuity to other parts and equipment?


well how would you practically do that then, if your wiring lights in T&E and don't need to have cpc continuity throughout the circuit but have metal switches for example how would you achieve that then? would you use 2 core cable around the lights and run a seperate cpc to the switches, come on it is obvious really that continuity is maintained for this practicably in a domestic situation T&E s are used so why the big issue, it is obvious why continuity needs to be ensured, I'm suprised at you fella on this one. whats the problem with maintaining continuity with the CPCs here then?
 
If the cable is accidentally screwed or chewed by vermin, there is no guarantee that both the line conductor and the CPC will be caught by the screw or vermin.
This is why, RCD protection is a method of providing additional protection for cables concealed in walls.
Are the downlights installed in walls by the way?
RCDs do not require a CPC to operate, if they did, then there would be no point in plugging your hedge trimmer into an RCD protected socket.
A CPC is not there to protect the cable.
It is there to earth exposed-conductive-parts which may become live under fault conditions, and to provide a path for earth faults which may occur in equipment conected to the wiring system.


I have a good Idea then, lets banish all CPCs and remove carpets in the house and replace with rubber mats and rcd everything and hope they work.
 
It's not a question of why, what or how it's done.
It's a question of whether the situation is dangerous or can give rise to danger.
If everything on the circuit that needs to be earthed is earthed, where is the danger?
 
No you said continuity of cpcs wasn't required in the circuit if exposed parts were earthed, I'm saying okay thats fair enough but in a domestic situation how would you make that Work if switches are metal? Obviously we would have to join the cpcs out and ensure continuity wouldn't we?
 
The metal parts of the switches are exposed-conductive-parts, they would require earthing and continuity of the CPC between them and the main earth terminal.
If you were to install 6 downlights in your living room, and feed them from your existing ceiling rose, would you need continuity of the CPC between all the downlights?
Why?
 
I would ensure all cables had an cpc connected yes, whether they were actually connected to the downlighter would be depending on whether they needed to be or not, usually they would be, but not always, however with your view we may as well wire the whole house in 2 core cable and run seperate cpcs to the switches as most pendants are plastic (1) not practicable and (2) unheard of, I say show me just one spark who wires a house without ensuring continuity of the cpcs is ensured, you just won't find one, so why the silly comments, the cable we use has a cpc, why not ensure it has continuity, it's school boy stuff, talk about overcomplecating a minor issue, if there is a cpc present then it is usuable if needed,if not still connect it so continuity is at all points just incase it is ever needed, we had a chat about this a few days back and regs were mentioned regarding cpcs in cables, I can't think of anyone not ensuring continuity, why the big issue?
 
No that is not my view at all.
I don't know personally of any sparks that would not ensure continuity of a CPC, although I could introduce you to some (myself included) who have run circuits with out a CPC.
However ther must be some out there that carry out this practice, otherwise we wouldn't have the OP, and I wouldn't have come across the very same thing myself on a number of occasions. Perhpas ther's just the one spark that does it, and I and the OP keep finding their work.
I'm at a loss as to how you find my comments to be silly, considering some of the comments you have made.
Yes the cable we use (if it's T&E) has a CPC.
One reason for not ensuring continuity, could be cost.
I don't think there is any need to discuss overcomplicating the issue, you seem to be doing a prety good job as it is.
By alll means connect the CPC in case it is ever needed. I don't have a problem with that.
Yes we did discuss a similar matter a few days back, yes the Regs were mentioned, however as no Regulation in BS7671 requiring that a cable incorporate a CPC exists, I think you may have misunderstood.

I'll reiterate.
There is no requirement in BS7671 for a CPC to be incorporated in a cable.
It is prohibited unless the manufacturer provides a specific termination, or in certain conditions where circuit conductors pass through the enclosure, to terminate a CPC in a double insulated enclosure.
Yes the 17th edition requires that a CPC be terminated at each wiring point and at every accessory in a circuit, however that does not mean that circuits wired to earlier editions of the Regulations, which do not have a CPC at every wiring point and accessory are unsafe for continued use.

Now I've asked a number of times for you to explain what you consider as being dangerous with the OP's scenario.
Is there any chance that you could answer?
 
I never said it was dangerous, However in modern wiring it is unusal IMO and not normal practice, as for bs 7671, I couldn't give a flying monkeys for that TBH regarding this instance, there is such a thing as good practice and cpc continuity in a circuit is one of those, I am aware some old cabling has no cpcs and plastic lugs are used in switches due to this, however we have departed from that and the conversation got around to modern methods concerning why cpcs needed to be connected and continuity assured, you tried to lecture us about it not being required unless exposed parts was evident, I agreed but asked you to confirm wiring methods in a modern domestic situation regarding this, you then tried to ask me a homework question about downlighters, I will look through the thread again but due to your commects regarding asking me specifically several times about explaining my views regarding the OPs question I will look again, I cannot recall this question previously, when it comes to a cpc in a cable, I will have to look back, but I think murdock gave a reg number suggesting it was required, well certainely in most instances at least, and in the domestic enviroment I'm sure this was one instance, so my question to you again would be if you wired a house then would you not use T&E and just use 2 core if pendants were the lights preferred by the customer and run a seperate cpc only to exposed parts/ or like the rest of the UK electricians ensure continuity of the cpc is carried out?
 
going back a few threads this was your comment Why does the CPC need continuity throughout the circuit?
If there's continuity to the parts and equipment that needs to be earthed, what is the danger if there is no continuity to other parts and equipment?

I asked how you would ensure exposed parts Ie metal switches would get earthed in this instant considering T&Es would be used, I just can't see a problem with this question and yet a huge debate has errupted haha
 
I never said it was dangerous, However in modern wiring it is unusal IMO and not normal practice, as for bs 7671, I couldn't give a flying monkeys for that TBH regarding this instance, there is such a thing as good practice and cpc continuity in a circuit is one of those, I am aware some old cabling has no cpcs and plastic lugs are used in switches due to this, however we have departed from that and the conversation got around to modern methods concerning why cpcs needed to be connected and continuity assured, you tried to lecture us about it not being required unless exposed parts was evident, I agreed but asked you to confirm wiring methods in a modern domestic situation regarding this, you then tried to ask me a homework question about downlighters, I will look through the thread again but due to your commects regarding asking me specifically several times about explaining my views regarding the OPs question I will look again, I cannot recall this question previously, when it comes to a cpc in a cable, I will have to look back, but I think murdock gave a reg number suggesting it was required, well certainely in most instances at least, and in the domestic enviroment I'm sure this was one instance, so my question to you again would be if you wired a house then would you not use T&E and just use 2 core if pendants were the lights preferred by the customer and run a seperate cpc only to exposed parts/ or like the rest of the UK electricians ensure continuity of the cpc is carried out?

If it's not dangerous, then there is no requirement to make a note about it.
If there is no requirement to make a note about it, then it doesn't warrent a code.
I don't think I'm lecturing, just stating my opinion.
Perhaps it was a homework question, did you answer it?
Murdoch quoted 411.8.5 and 412.2.3.2.
I would probably use terminal blocks and chock boxes and ensure continuity of the CPC.
 
The op stated the cpcs at each light had been cut, therefore unless he or she didn't clarify otherwise then My comment about ensuring continuity is merited, it sounded as if no cpcs were evident anywhere due to being cut, although some metal back boxes on switches have plastic lugs most don't, I suggested it would be a code 2 and need improvement, it is possible it is not the case, but unlikely, however knowing domestic wiring methods and materials I expect there are exposed parts unprotected on this circuit somewhere, as for the home work question, I think I have answered it however it was a poor question and not worthy of an answer, I was trying to talk to you about good practise and real life regarding modern installations, I understand you saying it wouldn't even be a code unless dangerous, but can't imagine any sparks doing a PIR or whatever it is called these days thinking it to be acceptable to not consider coding it, a short run to a plastic switch or light may be something which gets away with it, but wiring through to downlights without any cpc would get a mention on the certificate IMO and rightly so, as mentioned before we can always rip up the carpets and put rubber floors down, by the waY, I would never use a chock box ever, but maybe a terminal block, either way I would ensure continuity of a cpc in a domestic circuit whether plastic fittings or otherwise, as the cpcs were cut then at the very least a reconnection would be something to consider, again good practise IMO.
 
MDJ, the OP stated: All the earths at the downlights have been cut away, they are plastic downlights but surely it is still potentially dangerous if the earth doesn't exist ie.. Change to chrome fitting etc..... I marked this is a code 2, am I right or wrong??
The choice of codes was not because the CPC was not continuous, but because the class II fittings may be changed to class I at some point in the future.
Yes if the defect was that exposed-conductive-parts were not earthed, then it would warrent a code C2.
There's nothing to stop you mentioning the fact that the CPCs have been cut out at the down lights.
However applying a code to the situation is another matter.
You mentioned something in an earlier post about silly comments, and now you repeat your comment about rubber mats....
Why would you not use a chock box?
What would you use to enclose the terminal block if you were to use one?

Yes I found recently on an EICR a situation where I beleive it was seven downlights had been installed, and the bare CPCs had been twisted together.
I explained to the householder that I considered this to be poor practice and that it did not comply with the Regulations, I suggested that it should be rectified.
The cheapest option was to use terminal blocks, chock boxes and some G/Y sleeving.
I ended up using a whole pack of ten chock boxes, as there were some other connections in the lighting circuit which were not enclosed.
 
Last edited by a moderator:
I would use a JB with cable clamps actually, yes you can get them, I don't like chock blocks cheap and cheerful IMO, as for plastic down lights, I must have missed that bit, if so I apologise, I have never seen a plastic downlighter actually from memory, I have seen metal downlights without an earth connection though, although I would use a make with a terminal, I just can't think off hand now about a actual plastic downlighter, you wouldnt want to put a 50 watt dichoric in one would you haha, either the op is mistaken or I have been awake too long, Seriously I am not for one minute saying the OP is wrong, but I just cannot think of a plastic downlighter at this moment, a mental block perhaps, I expect it will come to me soon, if changing to a chrome fitting though and no cpc available then yes c2, even without a metal downlight in a house if cpcs were evident and cut off I would still mention it myself, I bet there are exposed parts in the circuit somewhere. I wouldn't just dismiss mentioning it on the certificate myself, not in todays world, good practise to ensure continuity is assured.
 
I would use a JB with cable clamps actually
Which kind of leads us back to the other discussion about using 2 core cable for double insulated equipment.
What cable would you use from the JB to the downlight?
 
depends on the down light, if it was metal a 3 core, if plastic which I cannot recall ever seeing ever TBH a 2 core, but the actual cpc of the 6242Y would be connected through in the JB right by the side of the downlight to ensure continuity to all parts of the circuit, which is my point, I am not saying actual down lights need to be earthed, but continuity needs to be at all points IMO, and yep I know your now going to argue if a foot of 2 core cable can be connected to a plastic downlight with no earth facility why cannot the whole circuit yawn.
 
I've no intention of arguing any such thing.
If you recall from the other thread, apparently 2 core cable is not allowed.
If you're that tired, perhaps you should call it a night?
 
yep the other thread did say that and it was very interesting, although murdock found some regs which suggested a 2 core was a problem there was some good arguments from others in the thread, and from memory it never got resolved properly.
 
Wow. that took some serious reading, my head actually hurts...whats a cpc? ha. I've literally got nothing to say, as ive forgotten half the convo already. Bed time.
 
Use plastic fittings on light fittings and switches write label stick to db stating no cpc to light circuit sorted..
cpcs may be present cavity of ceiling just not connected to light fittings.
Lights may be fed from Junction box so continuity may exist in rest of circuit who knows eh....
 
Thanks for all the comments guys, seems like a bit of a grey area, personally myself I coded it a C2 and the repairs have been done, personally I would like to see an earth at every fixture/fitting in an installation wether it is needed or not, needed for testing purposes alone IMO, thanks again very interesting read
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Code faults ????
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
nicsin02,
Last reply from
nicsin02,
Replies
35
Views
4,503

Advert

Back
Top