Carrying out an EICR and have discovered a lighting circuit has a borrowed neutral from ring main. No RCD as its old 3036 fuses but have a disagreement with my colleague who believes it should only be a C3 for improvement recommended. I was almost certain it be flagged as a C2. Anyone able to voice opinion (and who owes who a beer!)
 
alright grumpy, make sure you get out of the right side of that bed tomorrow! lol

I'll be the first to admit not testing between neutral and neutral and neutral at every light fitting i've changed.

IMO code 2
In your opinion code 3
I'm happy with that
oh come on......
its neither is it.....
what you do is note it......
and move on..
and whats this `testing at every point` thing n all...where shared neutrals are concerned.....
just do it at the board....IR between em......that`l find it....if its there....
 
evr heard of a safe iso?...
just stop it now will ya....

well if you only disconnect the lighting circuit your working on then safe isolation proceedures arent going to help you as you wont notice the borrowed neutral open circuit until you seperate the wiring at a connection point.
its code 2 all day long for exactly the reasons somerset gave.
 
314 of the regs...division of installation. Especially 314.4

Now the debate is going to be, the regs are non-stat / use common sense.

My opinion is my opinion, you're entitled to youres. Lets leave it at that, so this doesn't turn into another argument on this forum over the matter of opinion.
 
oh come on......
its neither is it.....
what you do is note it......
and move on..
and whats this `testing at every point` thing n all...where shared neutrals are concerned.....
just do it at the board....IR between em......that`l find it....if its there....

You've misunderstood me, what i mean is that I don't check for a borrowed neiutral everytime I have to change a light fitting,
As for meggering between them at the board - only if all switches are in on position and both mcb's are on in fuseboard, in fact its easy to miss by meggering
 
well if you only disconnect the lighting circuit your working on then safe isolation proceedures arent going to help you as you wont notice the borrowed neutral open circuit until you seperate the wiring at a connection point.
its code 2 all day long for exactly the reasons somerset gave.
what a load of old donkey cak this is....
so you conduct an EICR.....and the next guy comes along and sees the previous report......capish...
....
 
This is why all faults dont have pre determined codes, every situation and deviation from the regs are down to the inspectors discretion, but if i had to stand in a court of law and be asked how i came to my decision (not just on borrowed neutrals but other faults too) then i would want to err on the side of safety.
 

Reply to Code for borrowed neutral... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top