just done a EICR. good installation, approx. 10 years old. 16th ed.split board, lighting circuits non-RCD, on TT earthing. my query is this:
the Zs readings are high, due to the high Ze, insofar as , e.g. lighting circuits on 6A MCB each have a Zs higher than the max. permissible . should I C2 the high Zs readings, or give it a "pass" with a C3? your thoughts, gentlemen (and ladies).
 
I'd C2 that Tel, unusual to find that as back then the split board on a TT install would generally have a 100ma protecting the lighting circuits. It's definitely potentially dangerous as any metal switch or light fitting could have a fair voltage appearing under fault conditions while the MCB thinks about tripping.
yeah, i had to give a C2, if only to cover my back. a solution would be to replace the 2 6A MCBs with RCBOs. saves the cost of a new CU.
 
Is there a main switch s type rcd.? If so then NO code (depending on how high the result is) if no main switch rcd then i would be c2.
You MUST code missing 30mA additional protection where it is now required. But absolutely if there is no means of achieving earth fault protection then the installation has a potentially dangerous defect so C3 would be wholly inappropriate for that.
 
What else is on the non rcd side? Why not install main switch rcd s type instead of 2x rcbos?
on the non-RCD side are 3 MCBs. 2 lights and 1 smokes. there's small reason to have 2 lighting circuits as its a 1 bed flat, all on 1 floor. i'm going to suggest 2 x 30mA RCBOs and maybe piggy back the smokes from 1 of the light circuits. this will also make the buried cables compliant and the lack of RCD protection for bathroom fan and lights ( shower is on RCD side, and supp bonding in place, so I gave that bit a C3 ).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
code query
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
telectrix,
Last reply from
Midwest,
Replies
18
Views
2,646

Advert

Back
Top