Hi Everyone,

looking for some help on codes;

tested a doctors surgery and one of the DB'S is 15th Edition has a 300ma RCD main switch feeding water heaters, sockets and lighting circuits so none of the circuits are protected by a 30ma RCD does this justify a code 2 on the observations? or is it less than a code 2
because its in commercial premises?

Also one of the DB'S has a BS88 fuse feeding sockets am i right in giving this a code 2 ?

My experience in testing is mainly in domestic so I'm not really sure if the same apply's?

Cheers.
 
What you have to ask yourself is does this installation comply to the 15th edition. If it does then all you can give is a code 3 to any non compliance to the current edition.

PS Why do you think BS88 fuses feeding sockets is a non compliance.
 
Hi Everyone,

looking for some help on codes;

tested a doctors surgery and one of the DB'S is 15th Edition has a 300ma RCD main switch feeding water heaters, sockets and lighting circuits so none of the circuits are protected by a 30ma RCD does this justify a code 2 on the observations? or is it less than a code 2
because its in commercial premises?

Also one of the DB'S has a BS88 fuse feeding sockets am i right in giving this a code 2 ?

My experience in testing is mainly in domestic so I'm not really sure if the same apply's?

Cheers.

A BS 88 fuse is probably providing a far better closer protection than a MCB!! It's just that it's a one time only OCPD. So no code for the BS88 Fuse. The code 3's will only be relating to lack of 30mA RCD's...
 
A BS 88 fuse is probably providing a far better closer protection than a MCB!! It's just that it's a one time only OCPD. So no code for the BS88 Fuse. The code 3's will only be relating to lack of 30mA RCD's...

And that is only if they actually do require the additional protection in the first place.
 
What you should also take into consideration is the usage , its a doctors surgery critcal equipment in there , you wouldnt want a doctor to be using a de fib and the RCD trips , before coding asses the risks
 

Reply to Codes in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

@DefyG is right... I'm not fully sure what your boss is after as when doing single line diagrams I usually show the whole installation. Anyhow I...
Replies
4
Views
405
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top