Coding eicr in 11 year old hotel. | on ElectriciansForums

Discuss Coding eicr in 11 year old hotel. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

DBs located in every room.
7 x circuits in All DBs.
Im doing condition reports.
Many of the DBs have been installed as the pic attached. The top surface of the DB has been completely removed andbbutted up to ceiling. A large hole in the plasterboard with cables entering. No gland on the SWA feed also entering through the plasterboard.
C2s
-No swa gland
-fire barrier not made good where cables pass through ceiling.
- dust ingress entering from ceiling void due to method of installation.
-integrity of DB not maintained due to removal of top surface.

Other rooms have DBs mounted in cupboard. A large bush in top surface for cable entry and is mounted high level. Ip4x not maintained but only accessible via step ladder. Live parts potentially accessible, can get finger through but very unlikely.

C2
Mini fridge socket in every room has no rcd protection and is not labelled for specific use. Also the caretaker has mentioned its often unplugged and used by guests for other things. Another point alrough very unlike again on ground floor there is patio doors in all rooms, potential for use outdoors in a hotel room would you take this into consideration?

Thats enough for now. Plenty more obs for such a new installation.
 

Reply to Coding eicr in 11 year old hotel. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
718
Code 2 the armour is the cpc and that is very corroded.
Replies
2
Views
394

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top