Hi sparks.
Gas safe plumber here please be gentle.
Just went to a boiler breakdown. I traced the fault to the room thermostat so I linked it out on the pcb board in the boiler.
The boiler is working fine now. 2 year old B&Q combi.

While I was there I checked with my multimeter the supply to the boiler and had earth to neutral 230v and earth to live 0v.
I was too paranoid to switch the neutral and live in case I blew the board.
Should I have switched them? How come the boiler is working fine like that? Will it damage anything being like that? If I need to reverse the polarity, then why?
Thanks in advance
 
First thing I would do is check to see if it’s just the boiler that is connected up incorrectly or if the problem is back at the CU.

The boiler will work with a reversed L&N, but I think it should be checked out as if the reverse is in the CU, the live supply to all equipment in the property will be without any fused or MCB protection.
 
Last edited:
If the full installation has reversed polarity there are serious safety implications as the MCBs will only switch off the neutral so the circuit will still be live.

This needs looking at and confirming ASAP.

Also would reverse polarity on a boiler not make things colder??? :D
 
If I were at a site and found some kind of gas anomaly/problem I would advise the customer to get a gas safe person in. But then, I'm an electrician not a fitter.
 
That's just what I told the customer after reading Andy's reply, "call an electrician in to check the rest of the house" to only be told "I'm selling the house next year so I won't bother". Stinjy f**ker, and he's got 3 kids in the house.
 
There are several places,where the reversal could have occurred...would have been nice,to find out where,even if it was the leads to the multimeter :)
 
Can't see how the leads on the multimeter would make a difference. I had 230v between neutral and earth, why would it matter where the leads were plugged in

An analogy,would be if a ball-cock valve,were to be fitted,180 degrees out.:)

Definitely not having a pop at you,but you wouldn't be the first person to inadvertently place the meter leads in the wrong ports...i've done it,anyway.......so there,I'M Sparticus :cool:
 
An analogy,would be if a ball-cock valve,were to be fitted,180 degrees out.:)

Definitely not having a pop at you,but you wouldn't be the first person to inadvertently place the meter leads in the wrong ports...i've done it,anyway.......so there,I'M Sparticus :cool:
You need to have a read of what you have just written dood.
 
You need to have a read of what you have just written dood.

Yep,just done that...

The ball-cock analogy is correct,in as much as more water=open and less water=close,ie; in reverse :)

There is a nod to good manners,and an admission of a possible misconception,being a shared error,and,including oneself...

Oh,and a small,movie related joke,accepting i have been the first to mention this...

I think your comment is quite rood ;) (see what i did:rolleyes:)
 
Always good to work things out for yourself.

However ......... regardless of leads being reversed as our plumber friend stated he has 230 between neutral and earth . . .

Didnt Mean to offend.

Happy Friday.

Lurch
 
Hi fella,i read his readings,and because he was using the wrong device for conclusive proof,had not stated how and where,he applied the probes,and others had already mentioned getting a spark in,i was throwing in a non-confrontational reason,for errant results.

In truth,i just wanted to go round to his job,and see if a 4 week trained meter fitter,had LNLN the meter ;)

Thanks for the reply,if we don't keep the banter up,we might as well be in the Brexit talks :p
 
That's just what I told the customer after reading Andy's reply, "call an electrician in to check the rest of the house" to only be told "I'm selling the house next year so I won't bother". Stinjy f**ker, and he's got 3 kids in the house.

To cover yourself put your concerns in writing and keep a copy.
As far as the wiring regulations are concerned this would be classed as ‘potentially dangerous’
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales

Thread Information

Title
Combi Boiler reverse polarity
Prefix
N/A
Forum
Central Heating Systems
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
Subby,
Last reply from
davesparks,
Replies
19
Views
10,784

Advert

Back
Top