Afternoon all,

Just a confirmation question if i can. A mate as asked me to install a fused spur (in his kitchen) for a combi boiler he is having installed.

The CU is an old wylex, no RCD or MCB's, TNCS supply with what looks to be a 6mm earth supplying the board and 6mm bonding to gas and water. (The whole house is only on 3 ways - Sockets, lights and supply for old immersion heater)

If I was to run the cable from an existing socket in surface trunking, would this eliminate the need for an RCD? (OSG p22).

As this would be a modification to a circuit I understand I would also need to run new 10mm bonding to both services and run a new 16mm earth from the supply (which is in an outside cabinet along with the meter).

Thanks all!!
 
No as all skts now need to be RCD protected unless under supervision or label for a particular.

Also all the Bonding cables would need upgrading to the releavnt size.

Probably best to just put it on a plug top if all the alterations aren't possible.
 
i believe you will be ok as the regs say an exception is made for a specific labelled connection of a item of equipment just as the other guys say check your earth and test out!
 
No as all skts now need to be RCD protected unless under supervision or label for a particular.

Also all the Bonding cables would need upgrading to the releavnt size.

Probably best to just put it on a plug top if all the alterations aren't possible.

you are right about sockets but as the op is adding in a fused spur and its all surface then he does not need an rcd
 
Thanks all for your quick responses. It's always good to have a second opinion :D.

Just got to work out a way of getting the 16mm cable from the CU to the incoming supply.

Mucho apreciation!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Combi Boiler
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
6
Unsolved
--

Advert

Thread statistics

Created
Ponty Massive,
Last reply from
Ponty Massive,
Replies
6
Views
2,045

Advert

Back
Top