Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance
 
Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance

When you say Vulnerable equipment, i hope you have accounted for any dimmer switches, and removed them. Dimmers are (or should be) in the line conductor only, and no matter which test method you use, if they are in circuit, you WILL kill them.

Cheers...........Howard
 
Hi
Carrying out a whole board insulation resistance test , very large house and LOTS of vulnerable equipment so wish to do a L&N combined [ link busbar to neutral bar] on whole board. Each circuit is on a RCBO , how would i test this, do the neutral and earth fly leads of each RCBO need to be disconnected?
Thanks in advance


Disconnect L & N from each RCBO, link and then test to earth.
 
Dimmers are (or should be) in the line conductor only, and no matter which test method you use, if they are in circuit, you WILL kill them.

No, you won't kill them if you're testing L+N to E. I never have. If they have the same potential on input and output, which they will if L and N are connected together, then no problem.
 
They can only have the same potential on either side if you've bridged across the lamp?
Laurie


No, you won't kill them if you're testing L+N to E. I never have. If they have the same potential on input and output, which they will if L and N are connected together, then no problem.
 
Last edited by a moderator:
They can only have the same potential on either side if you've bridged across the lamp?
Laurie

If you leave the lamps in (no reason to remove them if testing L+N to E) then, since there's no significant current through the lamp when doing an IR test, the voltage on either side of the dimmer will be the same. This will apply in the case of standard GLS and halogen lamps, but may not be true for other types.
 
Which ever way you want to test is fine but with RCBO's and RCDSO you are far better removing the L & N from the units and then test.

The electronic internals are not compatible with IR testing even if it is fitted with a fly lead.

Post 4 answered the question IMO !
 
Which ever way you want to test is fine but with RCBO's and RCDSO you are far better removing the L & N from the units and then test.

The electronic internals are not compatible with IR testing even if it is fitted with a fly lead.

Post 4 answered the question IMO !
I Agree !
 
Going with post 4 too. Test each ct individually, it might take longer but at least you don't risk damaging the RCBO and having to replace it (pricey). Same goes for dimmers, if you ain't confident that they can withstand test take then out of circuit. I always IR at 250v on existing circuits & them ramp it up to 500v providing I don't get any unusually low readings.
 

Reply to Combined L&N IR test on all RCBO board in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
1K
  • Question
https://professional-electrician.com/technical/replacing-a-consumer-unit-in-a-dwelling-niceic/ All circuits should be tested
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top