I have been asked to carry out a job and would like to know if anyone can see any problems with what I intend to do

3 phase and neutral car lift supplied via 2.5 mm cable protected by 3 phase 20amp mcb I intend to come off 1 phase to supply a 13amp rcd protected twin socket to supply drills hand lamps etc

do any electricians see in problems in doing this I am an Niceic approved contractor and am stuck on this one
 
Yeah I thought it would be fine but have been told from someone that's it's not right as it is not indiviually fused

I've done it with people lifts to supply fuse boards and don't see any difference here

Cheers for the help
 
out of curiosity -i notice that the starters on these car lifts don't have overload protection fitted(2 i looked at recently anyhow)

why would that be or am i missing the obvious thanks
 
With regards to coming off a phase you will get loads of mixed responses, some do and some dont. I definately wouldnt hook off to supply a socket or some other without putting a seperate MCB inline but as its an RCD protected socket I would go with it. After all what is the neutral for on 3P+N circuits, it is only what happens inside control panels etc...
 

Reply to Coming off a 3 phase supply in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
670
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks