ive got lighting job at a workshop with bay lighting florescent the owner wants better lighting so i was thinking about replacing them with sodium lighting and where his florescents was giving out 200 watts, i i would get 400 watts sodiums problem is he wants test certificate but 3 phase board is old 25-30 years would i need to put rcd consumer unit as i am useing all old trunking,conduit and 9 gang switch
 
Simple answer is no you would not need to fit an RCD unless you needed it for additional protection.

It would seem that the installation is run in trunking/conduit and so would not need to be protected under regulation 526.6.6 or 526.6.7.

The only thing you will need to do is to make sure that the protection device will operate in the given time so your Zs will need to be done and calculated. Obviously Zs exceeds the sated time, then RCD protection can be fitted to counter this.

Just a piece of advise, you may find that the protection device be it fuse or MCB on an installation that old, may have been changed, and perhaps the original lighting circuit was designed as a B type MCB or a G type fuse and has been changed to C or M respectfully, so make sure your Zs is spot on.

Also make sure if that trunking/conduit is being used as the CPC, and I would expect it is on an installation that old, unless it's been rewired to fit CPC. You should check really the continuity of the installation using a ductor tester, but to confirm continuity you can do R2 with a wander lead, and your Zs test will confirm that you have a good EFLI path.
 
apart from the technical issues here, i would not consider sodium lighting in a workshop (too yellow). rather go for metal halide.
 

Reply to commercail lighting in the Talk Electrician area at ElectriciansForums.net

Similar Threads

You would have thought they'd have a switch to flick on and off to engage an override. Not on each PIR but an actual light switch
Replies
5
Views
932
Very small indeed, but I see it needs a 24v driver, or 12v if you look through the specs. Confusing. I’ve got cut-offs of LED white tape and...
Replies
2
Views
838
  • Question
When you did the further testing and got the 0.06 reading were the CPC's back in the consumer unit? Really when testing you should leave the...
Replies
8
Views
949
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K
I have an outbuilding a fair distance from the house. In this outbuilding I just want to have some lights, a small music radio/clock, and a...
Replies
0
Views
738

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks