Hi all.

I'm use to testing domestic property's and happy to do so, but been ask by a new company to do commercial and industrial pirs. Got a few questions.

When carrying out r1+r2 test, how do you complete this on lighting? Do you check at the last night and what happens if you can't get there?
Secondly when carrying ir test on lighting, do you disconnect all lights or do you not test between line and neutral?

Any help and other pointers would be great

thanks Dave
 
use a wander lead to measure R2 if it's awkward access. ditto with IR. short L and N , then test fron thare to E. sometimes with industrial you can't isolate a circuit, so just do the Zs and put LIM for the dead test readings.
 
Find end of line and test , if u can t test at one u can get to and make a note . Far as the IR testing line to earth disconecting all the fittings is not reasonably practical for a L to n test hope this helps
 
when i done 2394/5 you were told to test every light point in the circuit because the cpc could be twisted together and not connecteted to the light so you could miss this by just testing the last one , a know its a lot more work so is it worth doing it like that or not?
 
it all depends on what the client will pay for. if the budget is enough for a day's work , then you do what you can in 1 day.
 
Apply common sense (if there remains any in this country), agree with client what they are willing for you to test then note on certificate what you have and haven't done. Test according to site conditions and bs7671.
 
when i done 2394/5 you were told to test every light point in the circuit because the cpc could be twisted together and not connecteted to the light so you could miss this by just testing the last one , a know its a lot more work so is it worth doing it like that or not?

I was also taught this but I believe that in most circumstance it's too difficult to do this with timescale and labour therefore end of line test would be best in such a location.
 
Hi all.

I'm use to testing domestic property's and happy to do so, but been ask by a new company to do commercial and industrial pirs. Got a few questions.

When carrying out r1+r2 test, how do you complete this on lighting? Do you check at the last night and what happens if you can't get there?
Secondly when carrying ir test on lighting, do you disconnect all lights or do you not test between line and neutral?

Any help and other pointers would be great

thanks Dave

There Called EICR now but maybee Im being a bit picky

When doing industrial and commercial EICR you will come across a lot of limitations due to access of end of lines and not being able to turn power off , test at furthest accessible end points, note all limitations in the report and make sure the person ordering the report agrees with the them
 
Quite amazed at the amount of people here that think conducting industrial EICR's are going to be anything like the same as Domestic installations. You're entering a whole new ball game to be totally honest and a game where statutory regulations are just waiting to catch out the unsuspecting!! lol!!
 

Reply to Commercial and industrial help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
563
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
937

Similar threads

It applies to commercial if it shares the same supply as a dwelling.
Replies
4
Views
862
A small contracting company relies on word of mouth and good feedback / reviews. if you do work for 12 companies and have some spin off work from...
Replies
6
Views
470

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top