hi all.
I'm sure you've had this one crop up all the time but I need some advice.
I'm doing my first PIR on a commercial premises, golf course, with out buildings seperate. it is also the first PIR that the buildings will be having for insurance purposes. this installation was done to the 16th in 2003. there are 15 DBs around the building with majority being 3 phase. with the design there was supposed to be a planned maintenance package to look after the building. cost calling, there hasn't been.
my main questions are:
1. there are ring mains and radials feeding socket outlets around the building up to 32A. from observation the "cleaners" sockets and outside sockets seem to be the only ones on RCBO's. the other ones that are internal are not and there are a good 30+ circuits of these.
do these go down as a code 4??
or do they have to change these to comply with 7671(2008)??
the Zs reading are satisfactory.
2. with doing the forms, I have 15 DBs within the building. do these all go under one inspection report with the multiple test result sheets??
the obsevations and recommendations will not fit on one sheet, can I use a second observation sheet or must it be split onto a second inspection report??
3.the insurance co want it to conform to the 17th but it was installed to the 16th, how can I cover this with choice of words covering the install??
you can't force people to change their installations even though they are still safe.
4. outside metal bollard lights, do these have to be on RCBOs? cables are buried in ducts.
thanks in advance to who ever helps, seem to have dug myself in a little deep...
I'm sure you've had this one crop up all the time but I need some advice.
I'm doing my first PIR on a commercial premises, golf course, with out buildings seperate. it is also the first PIR that the buildings will be having for insurance purposes. this installation was done to the 16th in 2003. there are 15 DBs around the building with majority being 3 phase. with the design there was supposed to be a planned maintenance package to look after the building. cost calling, there hasn't been.
my main questions are:
1. there are ring mains and radials feeding socket outlets around the building up to 32A. from observation the "cleaners" sockets and outside sockets seem to be the only ones on RCBO's. the other ones that are internal are not and there are a good 30+ circuits of these.
do these go down as a code 4??
or do they have to change these to comply with 7671(2008)??
the Zs reading are satisfactory.
2. with doing the forms, I have 15 DBs within the building. do these all go under one inspection report with the multiple test result sheets??
the obsevations and recommendations will not fit on one sheet, can I use a second observation sheet or must it be split onto a second inspection report??
3.the insurance co want it to conform to the 17th but it was installed to the 16th, how can I cover this with choice of words covering the install??
you can't force people to change their installations even though they are still safe.
4. outside metal bollard lights, do these have to be on RCBOs? cables are buried in ducts.
thanks in advance to who ever helps, seem to have dug myself in a little deep...