P

Phil Mumford

Commercial periodic with loads of IT kit. One or two of the disboards have 4 pole isolators/main switches. I believe switching the neutral in some cases is incorrect and potentially dangerous.

When should you NOT switch the neutral conductor??

Thanks in advance for any info.
 
Hi There,

BS7671:2008 regulation 537.2.1.1 states that "Every circuit shall be capable of being isolated from each of the live supply conductors. In a TN-s or a TN-C-S system, it is not necessary to isolate or switch the neutral conductor where it is regarded as being reliably connected to Earth by a suitably low impedance."

I have never come across a situation where disconnecting the neutral is dangerous. In fact it's a bonus if you can, less risk of picking up a back feed through the neutral conductor for total isolation. Although according to the reg's not essential.

Cheers

Glenn
 
Not a fused neutral - this is 4 pole incomers on the 3 phase disboards. My inspecting engineer thinks there may be a problem with switching a neutral/PEN conductor in this scenario.

I don't see a problem - hence the post !
 

Reply to Commercial periodic question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

All good thanks, still trying to retire but still finding myself busy as ever. Hope you're well.
Replies
13
Views
980
In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top