Scenario: Commercial TPN distribution board down stream requiring type2/3 protection. Board is at full capacity and breakers discontinued etc. how are people getting around this? is it acceptable to be doubling up in the supply side of the main switch to feed separate enclosure with triple pole switch to control supply to SPD? cant see any reason why this would not be acceptable as long as ccc is met and connection is electrically and mechanically sound , interested to hear your thoughts

thanks
 
If the incoming supply is already fused at a level to meet the SPD's OCPD requirement then it seems a reasonable solution.

Is there any means of isolation before the board (if you are tapping off before the main switch)?

Can you keep the SPD cable lengths down to an acceptable distance (ideally 0.25m max for each cable so 0.5m loop L-E, etc, but certainly below 0.5m max so less then 1m loop) ?
 
Thanks for your reply , yes so the distribution board is fed from a MCCB panel board @ 63A. My plan is to match up the supply cable size , come off the incoming side of the main switch to feed a 63a triple pole MBC in a separate enclosure then loop over to surge protector all under 0.5m
 

Reply to Commercial Surge Protection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top