Isn't C3's only on a an EICR a satisfactory rating anyways?
Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual circumstances.
Whilst any C1,C2 or FI observations automatically result in an unsatisfactory outcome.the reverse is not also true.
Reply to Communal DB does it require RCD protection to be a sat EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...