Replacing DB’s with all singing all dancing RCBO’s
Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor DB supplies 1st Floor DB…16mm T&E installed IN fabric of building.
DB 1st Floor supplies Remote Garage Block 16mm T&E
With the Sub Main to DB 1st Floor Rcbo protected, also the Garage being Rcbo protected…there is no Selectively between Rcd devices
Is it possible to comply to Regs to install a MCB for the Sub Main to the 1st Floor DB
 
Last edited by a moderator:
Tricky. If you have good reason to know the route of the sub-main is not hidden less than 50mm of a wall surface, or if it has suitable protection against being accidentally nailed, etc, then no problem. But often that is impossible to determine if you can't see the route.
 
Tricky. If you have good reason to know the route of the sub-main is not hidden less than 50mm of a wall surface, or if it has suitable protection against being accidentally nailed, etc, then no problem. But often that is impossible to determine if you can't see the route.
Glad you could understand my writing, it’s difficult to put into correct wording… thanks …😎
 
Pretty sure we've debated this in here before and concluded it's a busted flush either which way. There seemed to be an option in electronic RCD style devices with intelligent monitoring and self-resetting functions........at a cost!
 
Yes, in practice you have three competing things to consider:
  • What the regs demand
  • What the overall risks are
  • What the customer is willing to pay/tolerate in decorating
Regs say 30mA RCD for any shallow cables without armour, etc, which after installation we can't tell. Having said that, BPG #4 only codes this risk as C3.

But if you try that on a sub-main you will likely get serious nuisance tripping that poses are real risk of injury from loss of lighting on stairs, etc, to spoiled food in freezers, etc. For cables that have been around for decades without a drilling incident that seems a backward step in safety. An auto-re-closer might help, but only if the trip threshold is occasionally hit as if you add a few leaky electronic things you might find a 30mA RCD won't stay closed at all.

To fix it (i.e. allow no RCD additional protection) means running new sub-mains in SWA or similar, and for many installations that is simply not happening due to cost, permission to run through other's property, and resulting redecorating costs.

It is a bit like the "per-1966 lights without CPC" question on CU replacement that comes up from time to time, but at least there the BPG #1 section 8 has industry-approved guidance about how to address related work that is non-compliant in the least-worst way, and that you could fall back on if challenged on your actions.
 
Last edited:
Renamed thread title to comply to Regs to install a MCB for the Sub Main to the 1st Floor DB. Please be more creative. It attracts more replies if the thread is well named. 😇🤓🧐
 
I'm sure this a few years ago, a 16mm feed in a fabric of a building, and was told to put in a lower fuse with a 60amp to a 40amp in switch fuse.
Except that does nothing in real terms, and can even be argued as making it potentially worse due to an increased disconnection time.
 
Thanks for all comments still debating how to solve this, i personally would install MCB, having an idea
the cable is installed under floorboards & drilled through joists preventing any penetration by nails. Saying that the mighty Few will decide the outcome.😎
 

Reply to comply to Regs to install a MCB for the Sub Main to the 1st Floor DB in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
815

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top