I’m currently problem solving a lighting circuit issue on a retail park.
newish install (12months old) IR of 12M Ohms across all three conductors, getting some very odd IR readings overall, I got a low reading between two separate disconnected cables, sent my meter off to be calibrated and came back fine, was due the 20th anyway.
I’m struggling to isolate the whole of a circuit because it means the block paving needs to come up and the cables to be dug up.
Split one circuit in half and lights removed, removed from the DB and got my 12M Ohm reading.
no lights on and the circuit holds fine, start plugging lights in and the earth leakage increases, running a TT supply so RCBO only, getting 47mA on start up with all lights dropping to 35mA constant (used MCB for testing purposes) remove lights and test separately on a test rig, and the earth leakage is 0.1mA.
I haven’t dug up every JB on this circuit but every one I’ve checked has been fine on all the other circuits I’ve been investigating, so leads me to assume it’s not a termination issue, plus these light have previously been working without any disturbance of the circuit in between.
my question is, has anyone else seen earth leakage under load through the cable? That’s what my tests point too but I’m going to rock the boat with my findings so I just want to get other people’s opinion before I let my findings known.
thanks
newish install (12months old) IR of 12M Ohms across all three conductors, getting some very odd IR readings overall, I got a low reading between two separate disconnected cables, sent my meter off to be calibrated and came back fine, was due the 20th anyway.
I’m struggling to isolate the whole of a circuit because it means the block paving needs to come up and the cables to be dug up.
Split one circuit in half and lights removed, removed from the DB and got my 12M Ohm reading.
no lights on and the circuit holds fine, start plugging lights in and the earth leakage increases, running a TT supply so RCBO only, getting 47mA on start up with all lights dropping to 35mA constant (used MCB for testing purposes) remove lights and test separately on a test rig, and the earth leakage is 0.1mA.
I haven’t dug up every JB on this circuit but every one I’ve checked has been fine on all the other circuits I’ve been investigating, so leads me to assume it’s not a termination issue, plus these light have previously been working without any disturbance of the circuit in between.
my question is, has anyone else seen earth leakage under load through the cable? That’s what my tests point too but I’m going to rock the boat with my findings so I just want to get other people’s opinion before I let my findings known.
thanks