"433.4 Overload protection of conductors in parallel
Where a single protective device protects two or more conductors in parallel there shall be no branch circuits or devices for isolation or switching in the parallel conductors "
I am in debate with another spark. I have installed 2x2.5mm twin & earth in parallel to supply two ovens (no hob just ovens) (long story why didnt use 4mm or 6mm) off a single 32A RCBO. The ovens are 3.5Kw each so total load of 7KW, without diversity thats a load of 30.43A. At the end of the parallel conductors I propose to install an cooker switch (isolation device) and terminate the preinstalled flex from the NEFF ovens into the load side of the switch . Installation method is clipped direct so 27A x 2 = 54A so no issues with current carrying capacity. The kitchen fitters usual spark has said they absolutely cannot be on the same OPCD (hasnt stated why) The only issue I can see is with 433.4 where branch circuits or devices for parallel switching cannot be be in the parallel conductors, but in this case would not be IN the parallel sections of the fixed wiring, only as a termination point. I can in fact seperate the parallel supply and run each oven off its own 16A RCBO but would like to know that I'm correct in stating it is perfectly acceptable if not somewhat unusual to have used parallel conductors and the arrangement above ?
Where a single protective device protects two or more conductors in parallel there shall be no branch circuits or devices for isolation or switching in the parallel conductors "
I am in debate with another spark. I have installed 2x2.5mm twin & earth in parallel to supply two ovens (no hob just ovens) (long story why didnt use 4mm or 6mm) off a single 32A RCBO. The ovens are 3.5Kw each so total load of 7KW, without diversity thats a load of 30.43A. At the end of the parallel conductors I propose to install an cooker switch (isolation device) and terminate the preinstalled flex from the NEFF ovens into the load side of the switch . Installation method is clipped direct so 27A x 2 = 54A so no issues with current carrying capacity. The kitchen fitters usual spark has said they absolutely cannot be on the same OPCD (hasnt stated why) The only issue I can see is with 433.4 where branch circuits or devices for parallel switching cannot be be in the parallel conductors, but in this case would not be IN the parallel sections of the fixed wiring, only as a termination point. I can in fact seperate the parallel supply and run each oven off its own 16A RCBO but would like to know that I'm correct in stating it is perfectly acceptable if not somewhat unusual to have used parallel conductors and the arrangement above ?
Last edited by a moderator: