Conduit as earth???? | on ElectriciansForums

Discuss Conduit as earth???? in the Australia area at ElectriciansForums.net

M

mickytuff

Hi all done some testing work at a hospital and the orignal wiring was done in metal conduit, now the zs figures tested all good, my question is can u calculate the r1 and r2 figure when their isnt an earth cable as such???
 
Good question,, as for r1 thats your line conductor, and r2 being your earth in this case the conduit. in this set up I use a wander lead and zero my meter with this long lead. then go around pokeing it onto every acessory's earth the highest reading I take as my r2 reading for the test cert
 
biggest probelm is if the conduit is broken you should really do a Zs at every point to confirm polarity and earth continuity ,what you should do is an r2 test instead of the r1r2 but note it on the test certs as conduit used as earth
 
So on the cert in the earth continuity box what would you put l/l n/n and then????? I agree doing the r2 method to confirm the earth, which is also confirmed by doing the zs test but do i leave the box blank or put n/a due to the nature of the wiring system used????, oh and thanku all for your ideas, all gratefully recieved, shud of said that 1st realy
 
I'm confused even further now.

Are you referring to the section for the cable sizes i.e 2.5/1.5 for a normal RFC??? Where conduit is used as the CPC, under the CPC size i enter 'K'.

For the measurements, L-L (r1), & N-N (rN) are as normal, for E-E (r2), again I put 'K' in the box.
 
When testing i use the amtech software and you can select the earth as conduit, you enter in the size of the conduit and it gives you a equivelant figure as a c.s.a of 80mm for 20mm conduit, meaning the conduit is acting like the size of a 80mm cable i presume, strange i know, but this figure cant be accurate, as the condiut could be 1m long or 30m in length, so this isnt realy accurate, the column i was reffering to was the ring final contuity part, what i've just said is the column your referring to, i.e the cable size part.
 
Ok nickblake here we go...............while testing with a megger multi, if you chose to test on notrip on your loop test, why do U have to connect all three leads, if you connect just line and earth it wont produce a reading and just say trp on the display, yet when you deselect no trip it tests fine with just two leads connected, so there you go, any body else had same problem???????????
 
Last edited by a moderator:

Reply to Conduit as earth???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
251
In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
457

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top