Good afternoon Gentlemen.I'm in the process of rewiring my garage so that I can join one of those fantastic schemes for my Part P.Question is this. looking at the OSG about conduit factors (Table 5D), it says about bends. Is this just bends in the actual conduit or does this include such things as 'elbows' and 'Tees'? The reson I'm asking is for example, it gives factors for 1metre runs with 4 bends, but none for 10 metre runs!!!Many thanks in anticipationLS
 
Tees and elbows should have inspection outlets which means you can pull in at these points so would not be included.

I remember, along time ago, attempting to pull through 20mm2 conduit, 3 * 2.5mm2 cables starting from a floor trunking 16m through 3.5 bends. I made the mistake of using a running coupler half way up the wall as opposed to a through box. I never did that again.

It doesn't take a very long length and a couple of bends to jam up the cables.
 
Last edited:
I never did get on with the newer conduit fill factor tables, it's like ''Double Dutch'' to me...lol!! I still use the old fill factor table as my starter guide, that and i suppose the experience that comes with the years of working on extensive conduit/trunking containment systems.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Conduit factors
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Litttle Shonet,
Last reply from
Engineer54,
Replies
3
Views
2,477

Advert

Back
Top