As i don't really do much proper conduit work, i have what may be an obvious question to some. Within a PVC installation, if you had 2 phases feeding a light switch for 2 lots of lighting, would there be a cpc pulled in with both the feeds, or is it done with just the cpc from one circuit at the switch?
 
Just playing devils advocate here Tel, but I can't see anything wrong with splitting a single CPC between two circuits so long as the csa is an appropriate measurement.
not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.
 
I'd take one CPC to the switch to earth the switch; if you 'had' to take a CPC for every live you might have each switch on a different cct so you could end up with about 20 cpcs in the switch, which would be silly.

Because it's being done in singles the CPCs for the lights can go straight from the CU to the lights, with the neutrals.
 
would that not contravene "all final circuits to be segragated" though Mr Skelton?

Check out reg 543.1.2. Where a protective conductor is common to two or more circuits...

not sure on that, but i prefer to see a circuit comprising of all 3 conductors. suppose at some time in the future, one of the circuits was no longer needed and disconnected. the other circuit would then be left without a cpc.

Me too. I agree, I would pull two CPC's through too. I'm just sayin', that's all ;)
 

Reply to Conduit installs in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
Thanks guys, I ran UF-B. Never handled 6/2 before, wasn't as difficult as I expected.
Replies
3
Views
930
  • Question
Thanks for the replies everyone, much appreciated. I've been in touch with our electrician as we're going to have him swap out some sockets from...
Replies
5
Views
609

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top