B

Bradzz

Hi all. I was wondering when completing a EICR when you have conduit as the cpc in a ring what do you input into the section r2. the end to end r2 reading. NOT THE R2.
do you leave that section blank. and just perform your R1+R2 reading, along with the end to end readings of the phase and neutral.
r1 .34/ r2 blank/ rn .34 / R1+R2 = your reading with the phase and conduit linked out at db.
Cheers all
 
Last edited by a moderator:
I wouldn't leave it blank, N/A instead.

Your R1+R2 test as you described would confirm the conduit is doing its job properly.

Just out of interest, how do you test your R1+R2 on a ring main in conduit that is using the conduit as CPC? Obviously, you can't to the usual figure of eight testing.

I've always done R2 tests in this situation.
 
Just out of interest, how do you test your R1+R2 on a ring main in conduit that is using the conduit as CPC? Obviously, you can't to the usual figure of eight testing.

I've always done R2 tests in this situation.

Very true Adam.

Impossible without isolating the conduit from the DB lol :tt1:

A case of typing away without thinking the question through first.
 
You can still check for spurs and interlinks in the ring by doing the test with L and N.
R1 + R2 is the resistance of the line and cpc so testing as I said is still valid. It's similar to testing a circuit that is parallel fed.
 
I would wander lead every socket just test the integrity of the joints on the conduit record the highest reading also in the cpc size column on the test cert you can put con.
 
You can still do the figure of eight test between L-N.
The L-E, R1 + R2, you might measure, using the long lead test at the furthest physical outlet.

It still doesn't guarantee that the conduit R2 is suitably connected. You may need to use an old test method such as an ac earth continuity tester which generates 50V ac at 1.5 times the design current of the circuit up to a maximum of 25A.

I haven't seen one of these for years.
 
You may need to use an old test method such as an ac earth continuity tester which generates 50V ac at 1.5 times the design current of the circuit up to a maximum of 25A. I haven't seen one of these for years.

Still very much available, we have used these Ductor type long lead earth continuity testers on all of the major projects i've been involved on, for testing our extensive metal containment systems . I do believe though, that on the most recent projects these testers were of American origin. Those that i've used in the past and in the UK, were i believe normally made by ''Clare industries''.....
 

Reply to conduit testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
323
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
851
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
973

Similar threads

  • Question
Also,if you had a duel box with a lighting cct on one side you would get a false reading.
Replies
2
Views
496

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top