Some basics:
For 90 degree bends (back of bend)
Start with a scrap piece of conduit preferably >1m. make a mark at a set distance from end (say 500mm). Put conduit in bender and line up with the start of your former, bend to 90, and remove from bender. Place conduit on floor and measure from back of bend (floor) to the end that you measured from. Say it's 448mm, this will give you a 'take up' of 52mm. Next time you simply add this 'take up' to your required distance, and you should be within a gnats tadger
. Would note above only applies if you are measuring from rear of bender (handle end).
If measuring from front of bender make your mark and slide through untill level with back of former + your conduit size (use an offcut of same sized conduit and level if unsure).
For offsets using 30 degree bends
Firstly the multiplier for 30 degrees is 2. So however much you need to offset conduit by, simply times it by two. i.e if you have a 200mm obstruction/level change, mark your bends 400mm apart (200 x 2).
For 45 degree bends just change multiplier to 1.41.
There truely isn't a set of instructions for conduit bending, and as previous members have stated "practice makes perfect". Gain and shrinkage should also be considered, but is often forgotten. hope this helps to reduce your wastage a little.
Kind Regards
Billy
Kind Regards
Billy