When calculating cable sizes...
When I want runs to be enclosed in conduit or trunking.
The grouping (Cg) makes (it) the cable size very large..
What am I doing wrong when calculating enclosed cable size.
An example would be a radial circuit ran with 4 other thermoplastic cables
In =20/ ca=1/Cg=0.65 /cf=1
It = 33.3 a
Using f6 tabulated ccc
Means I have to use a 10 mm2 cable
Looking at this if I wanted to use 2.5mm2 I can't use more than 1 cable in conduit???