hi all,
can anyone help me out please? i am studying for a BTEC in electrical installations and i have run up against a very basic problem. i'd be very grateful if anyone can explain...
basically, i'm trying to assess the cable rating for a socket ring main. i am confused because i thought cables had to be rated higher than the protective device, but everywhere i look i see 2.5mm t&e being recommended with a 32A protective device.
when i look at the tables in the electrician's guide, 2.5mm t&e appears to be rated at 21A when sunk directly into a wall.
surely the cable will get damaged before the circuit gets shut off?
i'm obviously missing something here,but i cannot see the wood for the trees.
for reference, i'm calculating the figures for 8 13A sockets on 24metres of cable. no grouping or ambient temperature correction, but the cable will go straight through a 100mm insulated wall in two places. system is TNS, voltage 230v.
thanks in advance,
tawraste:)
 
Hi

Hope this helps with what you are saying 2.5mm is rated at 20A for a radial circuit if its a ring main the cable rating is 40A. The radial should be protected by a 16A fuse and the ring with a 32A fuse

Good luck

Chris
 
Hiya

Yes indeed you are correct the fact that its a ring doubles the capacity. As a point of interest that may help you later no diversity allowed on the radial the ring is 100% then 40% thereafter

Regards

Chris
 
Hi

Hope this helps with what you are saying 2.5mm is rated at 20A for a radial circuit if its a ring main the cable rating is 40A. The radial should be protected by a 16A fuse and the ring with a 32A fuse

Good luck

Chris

Acat a 20A is acceptable for a radial on 2.5mm as long as area is not greater than 50sqM.
 
Last edited by a moderator:

Reply to confused about cable requirements in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
789
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
810

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
852

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top