Hi All,
Any chance of some help? I am installing a mirror unit in an office which contains two sockets to be used for models to do make-up etc. Plugged in to these sockets will be hair dryers and the like. The plug is a 16A commando type and the nearest dist board is 55m away. I have done the calculations as follows:
4000/230=17.39A
In = 20A
Cg = .5 as there are a number of cables from the db running through a pearling.
Ci = .78 for running through 100mm of insulation.
20/.5 x .78 = 51.28
As per table 4D2A, it states that a 10mm cable should be used. Surely that can't be right or am I missing something???
Any chance of some help? I am installing a mirror unit in an office which contains two sockets to be used for models to do make-up etc. Plugged in to these sockets will be hair dryers and the like. The plug is a 16A commando type and the nearest dist board is 55m away. I have done the calculations as follows: