guys,
ring wired in 2.5mm singles, contained in tray (roof) then conduit buried in wall down to dado trunking. end to end L 0.69 N 0.69 CPC 0.41
R1+R2 0.41
Zs 0.38
RCD trips within times
using megger 1730
as far as I can tell the CPC is 1 run to outlets no connections onto tray/conduit etc so wouldnt have thought parallel paths would be considered however I have been wrong many times before
unable to gain Zdb of board as not allowed to turn off
ring wired in 2.5mm singles, contained in tray (roof) then conduit buried in wall down to dado trunking. end to end L 0.69 N 0.69 CPC 0.41
R1+R2 0.41
Zs 0.38
RCD trips within times
using megger 1730
as far as I can tell the CPC is 1 run to outlets no connections onto tray/conduit etc so wouldnt have thought parallel paths would be considered however I have been wrong many times before
unable to gain Zdb of board as not allowed to turn off