One_of_them

guys,

ring wired in 2.5mm singles, contained in tray (roof) then conduit buried in wall down to dado trunking. end to end L 0.69 N 0.69 CPC 0.41
R1+R2 0.41
Zs 0.38
RCD trips within times

using megger 1730

as far as I can tell the CPC is 1 run to outlets no connections onto tray/conduit etc so wouldnt have thought parallel paths would be considered however I have been wrong many times before


unable to gain Zdb of board as not allowed to turn off
 
Last edited by a moderator:
May i ask how singles are used on tray and how you came about your R1+R2 result and if the conduit is metal

well its the tray with lid dont know how much more you want me to tell you?
cross connected at board. conduit is not used as the CPC if this is where you are going?
conduit is metal
 
If the conduit is connected to metal clad sockets then the first socket is going to be joined to all the other metal clad sockets through the CPC and the conduit hence having a lower R2
 
sockets are in dado (sorry that should be in the beginning bit)
tray runs in roof, conduit buried in wall to behind the dado and then to sockets
 
Has anybody ever seen it so you would run a CPC from board to tray, rely on this and conduit for cpc, then run a new CPC cable at the end of conduit onto the sockets?? Effectively saving on a bit of cable length?
 
Has anybody ever seen it so you would run a CPC from board to tray, rely on this and conduit for cpc, then run a new CPC cable at the end of conduit onto the sockets?? Effectively saving on a bit of cable length?

I have seen it done like this, and IMO it is acceptable, however personally I would usually use conduit/trunking for CPC only if it it was continuous to each socket, If it was in the situation you described, I would begrudingly run a cpc in with the other singles.

Has the job you are on been done like this? hence your low R2
 
thinking about it, is it not likely that the dado was added later over the original conduit drops (which were utilising the tube as a CPC), hence they have just extened the CPC from the original socket positions using G/Y singles?
 
I have seen it done like this, and IMO it is acceptable, however personally I would usually use conduit/trunking for CPC only if it it was continuous to each socket, If it was in the situation you described, I would begrudingly run a cpc in with the other singles.

Has the job you are on been done like this? hence your low R2

to be honest I aint pulled it apart that much to confirm. It was just supposed to be a simple addition of a couple of sockets. Fairly new build office block to.
As I started this thread it just dawned that maybe this is something that might have been done. I have never seen it but I can understand it been acceptable but not how I would ever do it. With the readings I got I believe circuit to be safe so I'm not too worried, just confused.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
confused with results
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14
Unsolved
--

Advert

Thread statistics

Created
One_of_them,
Last reply from
One_of_them,
Replies
14
Views
1,797

Advert

Back
Top