One_of_them

guys,

ring wired in 2.5mm singles, contained in tray (roof) then conduit buried in wall down to dado trunking. end to end L 0.69 N 0.69 CPC 0.41
R1+R2 0.41
Zs 0.38
RCD trips within times

using megger 1730

as far as I can tell the CPC is 1 run to outlets no connections onto tray/conduit etc so wouldnt have thought parallel paths would be considered however I have been wrong many times before


unable to gain Zdb of board as not allowed to turn off
 
Last edited by a moderator:
If the conduit is connected to metal clad sockets then the first socket is going to be joined to all the other metal clad sockets through the CPC and the conduit hence having a lower R2
 
Has anybody ever seen it so you would run a CPC from board to tray, rely on this and conduit for cpc, then run a new CPC cable at the end of conduit onto the sockets?? Effectively saving on a bit of cable length?
 
Has anybody ever seen it so you would run a CPC from board to tray, rely on this and conduit for cpc, then run a new CPC cable at the end of conduit onto the sockets?? Effectively saving on a bit of cable length?

I have seen it done like this, and IMO it is acceptable, however personally I would usually use conduit/trunking for CPC only if it it was continuous to each socket, If it was in the situation you described, I would begrudingly run a cpc in with the other singles.

Has the job you are on been done like this? hence your low R2
 
I have seen it done like this, and IMO it is acceptable, however personally I would usually use conduit/trunking for CPC only if it it was continuous to each socket, If it was in the situation you described, I would begrudingly run a cpc in with the other singles.

Has the job you are on been done like this? hence your low R2

to be honest I aint pulled it apart that much to confirm. It was just supposed to be a simple addition of a couple of sockets. Fairly new build office block to.
As I started this thread it just dawned that maybe this is something that might have been done. I have never seen it but I can understand it been acceptable but not how I would ever do it. With the readings I got I believe circuit to be safe so I'm not too worried, just confused.
 

Reply to confused with results in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
411
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top