Ruby B
-
As a newbie to this forum, I'm hoping that someone can help me understand a particular aspect of the EICR that was done on behalf of the previous owners of my current house. At the time (which I admit was some while ago) I was slightly confused by it but in all the chaos of buying the house, I put it to the back of my mind.
The summary (section E) states that the condition is 'Good' and that the overall assessment is 'Satisfactory'; however, there is a code C1 in section K Observations on the kitchen sockets circuit which says 'Excessive loop impedance' (further investigation required = No). This seems to contradict the 'satisfactory' assessment?
Also, looking at that particular circuit's details, it says Max permitted Zs of 1.09 and Maximum measured earth fault loop impedance of 0.82. I don't claim to understand what this is so in my simplistic way, 0.82 is less than the maximum so isn't that OK? There is an entry for the other sockets which also has a Max permitted of 1.09 and a measure of 0.76 so not too dissimilar.
I would be grateful if anyone could tell me if the installation should have been marked as 'unsatisfactory'. Thanks
The summary (section E) states that the condition is 'Good' and that the overall assessment is 'Satisfactory'; however, there is a code C1 in section K Observations on the kitchen sockets circuit which says 'Excessive loop impedance' (further investigation required = No). This seems to contradict the 'satisfactory' assessment?
Also, looking at that particular circuit's details, it says Max permitted Zs of 1.09 and Maximum measured earth fault loop impedance of 0.82. I don't claim to understand what this is so in my simplistic way, 0.82 is less than the maximum so isn't that OK? There is an entry for the other sockets which also has a Max permitted of 1.09 and a measure of 0.76 so not too dissimilar.
I would be grateful if anyone could tell me if the installation should have been marked as 'unsatisfactory'. Thanks