vincentv

I have a motor which is 3 phase. The power connection has 4 wires which is L1,L2,L3 and E.
And the power source we have is a 5 connection supply which has L1,L2,L3,N and E.

I accidently connect the E wire to N of the supply, and turned the power on. The cause the workshop power supply to tripped. After turning on the main supply and do the connection correctly. E connection of motor to E of supply the motor is not working.

Just wondering what i did, by connecting the motor E wire to N supply has damaged the motor or burn the motor?

Cheers
 
If the motor was ok to start with then this would have only tripped an rcd device(if you had one upstream), but shouldn't trip an mcb and making the correction when you realised should have rectified it.
What tripped? What size and type is it? What size is the motor? Are you starting it Direct on line? Is it connected Star or Delta?
 
That is the problem.. i dont know if the motor was ok or not to start with.
I think it was the main circuit breaker tripped. What is a RCD?
All i know is that the motor needs 460V 60Hz power supply.

Since the main circuit breaker tripped, this shouldn't have damaged or burn any fuses to the motor..

Correct me if i m wrong..

Cheers
 
Note! If you did as you say you did then it wouldn't have any adverse effect on the motor, do you get power to the motor now?

Where you from by the way 60hz isnt our normal 50hz is ours here in UK not that it makes any difference, an mcb or other type of fusing device trip with overload or short circuit and rcd monitors earth leakage so a link between N/E would trip this and they are commonly found at the front end of supplies so when they trip you lose power to multiple circuits.
 
Last edited by a moderator:
Note! If you did as you say you did then it wouldn't have any adverse effect on the motor, do you get power to the motor now?

Where you from by the way 60hz isnt our normal 50hz is ours here in UK not that it makes any difference, an mcb or other type of fusing device trip with overload or short circuit and rcd monitors earth leakage so a link between N/E would trip this and they are commonly found at the front end of supplies so when they trip you lose power to multiple circuits.

Agree where are you from, USA by any chance?

An RCD is the same as a GFLI

That is the problem.. i dont know if the motor was ok or not to start with.
I think it was the main circuit breaker tripped. What is a RCD?
All i know is that the motor needs 460V 60Hz power supply.

Since the main circuit breaker tripped, this shouldn't have damaged or burn any fuses to the motor..

Correct me if i m wrong..

Cheers


What do you mean by this comment the must be something wrong for the main breaker to trip in the first place.
 
Last edited:
I am from Brunei. We should have the same standard as the UK.

Now we are having problem with the motor not working. So need to verify what i did, is not the cause of failure.

Any explanation why the MCB tripped?

Cheers
 
I am from Brunei. We should have the same standard as the UK.

Now we are having problem with the motor not working. So need to verify what i did, is not the cause of failure.

Any explanation why the MCB tripped?

Cheers
If it was an mcb that tripped and not and rcd then it seems a fault must have already been there to start with,using a multi-meter and a insulation tester to confirm field coil resistance and insulation to earth would be a good next step,the connections you made would not have damaged the motor in anyway but their are other installation safety issues why it shouldnt be connected this way but as i said it wont have damaged the motor, we run at 50hertz 400/415 volt in UK so if you are the same then the motor is rated wrong to start with.
 
Last edited by a moderator:
Could the connection of E of the motor to N or the supply causing the MCB to trip?

After switching the E of motor back to E of Supply. This didn't trip the MCB..

Any explanation to this?

Cheers
 
Could the connection of E of the motor to N or the supply causing the MCB to trip?

After switching the E of motor back to E of Supply. This didn't trip the MCB..

Any explanation to this?

Cheers
As mentioned before this is the characteristics of an earth leakage device(rcd) and not and mcb and you said you lost alot of power to other circuits which again is common with rcd's and mcb normally protects individual circuits, was it a main switch that tripped which supplies a fuse board or an individual circuit mcb that tripped.
What is the kw rating of the motor?

How are you powering the motor is it 'Direct on line' so its runs straight away when you switch the isolator on or is it through a contactor with an overload on it and start/stop buttons.
Its possible the motor is rated to big and it took out the mcb on start up as well as the overload on the contactor, you may have switched the power on and not reset the overload, thus need to know motor rating kw for you supply, size of mcb that tripped, overload rating if fitted, is motor starting up on load or off load just to name a few questions also how are you turning motor on.
Without under-mining you it seems this is above you and with respect you shouldnt be doing this yourself if the above questions are not obvious to you as mistakes in this field can be costly but we will help where we can
 
Last edited by a moderator:

Reply to Connected wrongly.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
546
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
990
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
921

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
421
  • Question
I believe that it is incorporated into the 5 days. But will double check. Thanks.
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top