I`ve re-wired a house and was going to keep it as a TT system. The house is in the country and this is what they had before I re-wired. The electrician testing and signing of the installation said the main earth can be connected at the neutral in the head? Where would I connect this up? Or should I leave it as a TT?
 
It sounds to me that the installation supply may have been upgraded from a TT (overhead cables) to a TN-C-S (PME) system. This is something you could clarify with the distributor.

If it has been upgraded to a TN-C-S system then the inspector is correct, you can connect in at the supply head. Basically the distributor should have created a main earth terminal which pokes out of the supply head, next to the neutral termination. This is where you connect your earthing conductor. I would suggest you would need a 16mm earthing conductor to supply your consumer unit. It may be 10mm at present. You can then do away with the earth electrode. You may get a more stable and reliable earth than a TT system, it will certainly be a lower value resistance path.

The image below shows an older type of PME supply with the earth connection. Some of the recent distributors heads have a seal on the access to the earth block and they will put a Main Earthing Terminal block nearby for consumer use.

***CAUTION*** If you have any outbuildings supplied, and they contain extraneous conductive parts, you would not continue the TN-C-S earth into those. You would still employ a TT based system for those separate outbuildings and give the outbuildings an earth rod, with RCD protection.

Earthing is a complex area and it is vital you use a qualified person to undertake and test the works.

[ElectriciansForums.net] Connecting an earth
 
Last edited by a moderator:
Thanks for your help.

It looks like a fairly new SWA coming into the house. I took the cover off the head and found the neutral link. There is terminals but not one that pokes out of the supply head. Should I connect up inside the head? Maybe I`ll let the tester connect the earth.
Thanks again.
Andy
 
What you a re describing is a newer type of TN-C-S (PME) head of which I have no piccies, however the principle is the same... They just protect the connection under a little access flap. Your tester should be able to do an external earth fault loop impedance measurement at the head, to determine if the system is set up as a TN-C-S. If in doubt clarify with the local supplier... its usually just a quick phone-call... The fact that you have a new incoming cable sounds as if it has been upgraded.
 

Reply to Connecting an earth in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
702
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
718
  • Question
Hi, How did you get on with the wiring?
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top