oc1968jib

Could you help please?

As indicated above I have been asked to connect up one of the above units, which has a gas and water connection at it as well............. Supply voltage is given as 400v, 3N, 50/60. Amperage is given as 17.5.

I want to be clear on the cable size required, the type of isolator to be fixed at the unit end of the supply, as well as any help about the type of a possible safety cutout switch to be located next to the appliance.

I ask a lot and I am aware that some might be saying, "do you want us to connect it for you too?".

I would be grateful for enlightenment here.

Thanking you in anticipation.
 
if it'17.5A per phase, then 2.5mm cable on a 20A breaker is your starting point. then check VD and Zs values to ensure that 2.5mm is correct. a TP&N rotary isolator local to the fixture sounds logical.
 
if it'17.5A per phase, then 2.5mm cable on a 20A breaker is your starting point. then check VD and Zs values to ensure that 2.5mm is correct. a TP&N rotary isolator local to the fixture sounds logical.

Thanks for taking the time with your reply. Very helpful and prompt.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Connecting an Electrolux air-o-stream - level B; Combi LW 10 GN 1/1
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
oc1968jib,
Last reply from
oc1968jib,
Replies
2
Views
1,187

Advert

Back
Top