Hi,

I am installing an outside socket but had a question about how I can connect it to the internal supply. I have tried to represent my options/plan in the attached image. Are there issues with either of these approaches?

Additionally, does this work need to be approved/signed off in anyway or can it be done as a DIY job?

Thanks

[ElectriciansForums.net] Connecting outside socket to internal supply
 
scrub top pic. that's for wimps.
you don't need a FCU as long as the internal socket is not a spur, and there's only 1 outside socket (single or double). it also only needs to be an RCD socket if the house ring final is not RCD protected in itself. a Minor Works Cert. is desirable, but it's not notifiable work under part pee.
 
Also what cable are you taking to your socket? Pic says "swa 2.5mm2 t/e" which are two different cables? Needs to be 2.5mm 3core swa scrub the t/e bit
 
How the frig are you going to terminate that swa cable?

I’m not even sure you need swa
 
How the frig are you going to terminate that swa cable?

I’m not even sure you need swa
Take the spur cable straight outside fit a IP rated SFS nd take the SWA to the ip rated twin socket, gland into the spur and the twin socket
 
Sorry Pete
I can’t understand how the swa is going to be terminated in too the plastic outside socket and the switch fused spur, and still have fault protection with the armour ?
And why is a switch fused spur even needed.


And why swa?
 
Sorry Pete
I can’t understand how the swa is going to be terminated in too the plastic outside socket and the switch fused spur, and still have fault protection with the armour ?
And why is a switch fused spur even needed.


And why swa?
outside socket remote from house, ergo... SWA. what's the problem with terminating i a IP65 socket box?
 
how remote is remote?

There’s no reason it has to be swa.
 
scrub top pic. that's for wimps.
you don't need a FCU as long as the internal socket is not a spur, and there's only 1 outside socket (single or double). it also only needs to be an RCD socket if the house ring final is not RCD protected in itself. a Minor Works Cert. is desirable, but it's not notifiable work under part pee.

Thanks. Although for wimps :) is it viable? Allows me to plug and unplug as needed and not mess with a spur off the socket which is a little way from the wall.

I am actually looking to do this in two different places so may do a different approach in each based on use case.
 
how remote is remote?

There’s no reason it has to be swa.
Quite right you could use conduit, but SWA is easier to install.
 
so, if on a plug top, you'd not fix T/E into a plug top, would you. if you did i'd come all the way down to that den of iniquity (london) and spank your arse.
 

Reply to Connecting outside socket to internal supply in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
158
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top