I am thinking of installing a steam cabin which requires a 16 amp supply.
Power connection, Inside my airing cupboard, where once was installed the HW cylinder there is the old power outlet, the 4 mm wire comes from the consumer unit with a dedicated 16 amp MCB.
Can it be increased to a least 20 amps?
Can there be installed an insulated consumer unit like Mk sentry 4 way with the requested 16amp RCBO, 10 or 16 amps RCBO for a loft socket, and a 6amp RCBO for a light line.
Any comment to this project will be highly appreciated.
Thank you
 
The only thing is if the supply is 4mm^ T+E and is buried in a stud wall to method 103 then your max current carrying capacity is only 17.5 amps so check that.

Can I ask why your are wanting to fit a 4 way board to 20amp (if possible) supply. It's not a good design having the 16amp steam cabinet, then a 13amp socket and a light on just a 20amp supply. But as the socket and the lights are in a loft you might get away with it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
connection for shower cabin
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
ggman,
Last reply from
daniel hill,
Replies
4
Views
2,230

Advert

Back
Top