G

gjb1979

I know that it is wrong to just use a connector block and tape it up. However, I really can't find the reg / regs that state this.
Can anyone point me in the wright direction?
I like to know exactly why Im doing what Im doing.
Cheers
 
Hi, welcome to the forum.
BRB, 526.5 is the regulation you're looking for.
Any type of tape or sleeving is defined as supplementary insulation, even if it completely encloses the termination it is NOT an enclosure, nieve people in the trade would have us believe otherwise.
The other trap the inexperienced can fall fowl of is 526.5 (iii) an enclosure can be PARTIALLY formed or COMPLETED with non-combustible building material tested to BS 476-4, the enclosure CANNOT therefore be made totally from building material. The most common infringement of this is a crimped termination, covered with supplementary insulation (eg. heat-shrink sleeve) and buried directly in the wall with building material (eg. plaster).
 
Last edited by a moderator:
I disagree with your second comment mate. If you crimp a connection, and that connection is electrically/mechanically sound, then for me, 2 layers of heat shrink is the best joint that cable could have. Gita be the stuff that has glue though. I'd rather that any day than a JB in the ceiling. Now if that does'nt comply, then I will list is a departure. I've jointed plenty of underwater cables using the above method, and they outlast the cable itself.
 
I disagree with your second comment mate. If you crimp a connection, and that connection is electrically/mechanically sound, then for me, 2 layers of heat shrink is the best joint that cable could have. Gita be the stuff that has glue though. I'd rather that any day than a JB in the ceiling. Now if that does'nt comply, then I will list is a departure. I've jointed plenty of underwater cables using the above method, and they outlast the cable itself.


Quite agree with you John, this is one of the deviations from BS7671 that I believe that you could always argue in court mate. The only arguement against it is that 'technically' you could break the joint if you were to pull it though conduit/trunking.
 
Never liked tape or connector joints so I carry some choc blocks with me and when I have to repair say a spotlight and find a connect joint I deem this as exposed live parts and as you say make sure the joint is electrically and mechanically sound (14th edition) then fit the chock box yep it adds ÂŁ2 to the bill but that keeps me on the safe side and I have had no complaints otherwise even although it is or was pretty standard procedure to fit connector only and if you were posh you put insulation tape around it. Also to highlight years ago earth sleeving was very expensive stuff because the wholesaler knew you needed it plus if it turned up on a site it was snaffled before you could use it but yep things have moved on and there is no excuse not to fit an inline joint box or earth sleeving.
 

Reply to Connector Block Clarification in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Written in clauses are essential, but should be fairly standard fare to a solicitor. A similar situation exists around where I live with regard to...
Replies
9
Views
587
C
  • Article
Pressure reducer/regulator for plastic water line? Good evening, Wondering if i could get a little guidance, I have a 3/8 plastic line running...
Replies
0
Views
159
carpetguardian
C

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top