hi, this morning went to test and inspect a conservatory installation. recently done. explained to client that i could not sign off an EIC as i didn't design or install it. all i could do was to report on the installation as i found it ( thinking PIR ). what i have found is.
extension to kitchen ring final feeding 4 DS/O. RCD protected in split board ( 16th Ed. )
10 GU10 downlights fed from d/s lighting, no RCD
12 ELV LED's fed from a single transformer.
Faults/ deviations:
1. no grommets in S/O back boxes
2. ring final between 2 S/O's chased in behind skirting board ( non safe zone )
3. kingspan insulation tight around GU10's ( non fire rated )
4. cpc's cut off on GU10's so unable to read Zs. ( GU10's are class 2 )
5. transformer and any JB's are inaccessible without cutting out ceiling
client has agreed cost for fitting RCD kit in CU to bring up to full RCD protection. and to cut back the kingspan and buy a set of LED GU10's.
Zs readings on S/O 's good at 0.7ohms. IR readings >99M.
just think that have to do PIR, but unsure what code for 2 and 4 above. i would give 1 and 5 a code 4.
any thoughts lads?
extension to kitchen ring final feeding 4 DS/O. RCD protected in split board ( 16th Ed. )
10 GU10 downlights fed from d/s lighting, no RCD
12 ELV LED's fed from a single transformer.
Faults/ deviations:
1. no grommets in S/O back boxes
2. ring final between 2 S/O's chased in behind skirting board ( non safe zone )
3. kingspan insulation tight around GU10's ( non fire rated )
4. cpc's cut off on GU10's so unable to read Zs. ( GU10's are class 2 )
5. transformer and any JB's are inaccessible without cutting out ceiling
client has agreed cost for fitting RCD kit in CU to bring up to full RCD protection. and to cut back the kingspan and buy a set of LED GU10's.
Zs readings on S/O 's good at 0.7ohms. IR readings >99M.
just think that have to do PIR, but unsure what code for 2 and 4 above. i would give 1 and 5 a code 4.
any thoughts lads?