hi, this morning went to test and inspect a conservatory installation. recently done. explained to client that i could not sign off an EIC as i didn't design or install it. all i could do was to report on the installation as i found it ( thinking PIR ). what i have found is.

extension to kitchen ring final feeding 4 DS/O. RCD protected in split board ( 16th Ed. )

10 GU10 downlights fed from d/s lighting, no RCD

12 ELV LED's fed from a single transformer.

Faults/ deviations:

1. no grommets in S/O back boxes
2. ring final between 2 S/O's chased in behind skirting board ( non safe zone )
3. kingspan insulation tight around GU10's ( non fire rated )
4. cpc's cut off on GU10's so unable to read Zs. ( GU10's are class 2 )
5. transformer and any JB's are inaccessible without cutting out ceiling

client has agreed cost for fitting RCD kit in CU to bring up to full RCD protection. and to cut back the kingspan and buy a set of LED GU10's.

Zs readings on S/O 's good at 0.7ohms. IR readings >99M.

just think that have to do PIR, but unsure what code for 2 and 4 above. i would give 1 and 5 a code 4.

any thoughts lads?
 
IMO FWIW ;)

With No 2 i would code that as 2. Although you have effectively taken care of it, or will be, by installing an rcd.
With No 4 if you are unable to prove an effective earth at the fittings then i would go with a 2 again.
 
my confusion is that the fittings are class 2 and don't need cpc. it's the fact that the cable doesn't have continuous cpc.
 
There should be a cpc terminated at the accessory/luminaire 412.2.3.2, is it a safety risk or a non-conformity?

I'd say the latter and code 4.
 
IQ, i can't see a safety issue with it. it might just be that the cpc's are connected through in JB's but can't access due to kingspan above ceiling. i have pencilled in a code 4. malcolm has sent me a pm, suggesting a code 4 as well. i think fitting the RCD is the biggest issue as the install was done supposedly to 17th.
 
Last edited:
But if it had been wired in 2 core would that still be a code 4 ? If you can't test the cpc you can't prove it's continuity especially as the JBs are inaccessible. (tin hat on lol)
 
But if it had been wired in 2 core would that still be a code 4 ? If you can't test the cpc you can't prove it's continuity especially as the JBs are inaccessible. (tin hat on lol)

Take the tin hat off! Lol

It's a valid point but seeing as the cpc is there to take account of the possible replacement by the user of class II equipment by class I equipment, does a danger exist in the installation in it's present form?
 
agree. if the fitting don't need a cpc, then why should the cable have a cpc. i,m going to give it CODE 4. same with the grommets and the cable behind skirting board. the numpty has also used those stupid flat plate sockets which are "designed" to stick out proud as they are too deep for 25mm back boxes.
 
Personally Tel I would not code the grommits. If there is no damage to the sheath and therefore it would not contravene reg 522.8.1.

Grommits are good practice but not compulsory.
point taken , malc. don't want to pull it down too much as client has other work for me.
 
Take the tin hat off! Lol

It's a valid point but seeing as the cpc is there to take account of the possible replacement by the user of class II equipment by class I equipment, does a danger exist in the installation in it's present form?


Well once the full upgrade on the rcd protection is done i would agree, but if it was not rcd protected at the time of the PIR then would think there was more likely to be a risk.
 
i,m going to fit the RCD wednesday and will do the pir after it's in. readinds so far are on the back of a smoke packet so i don't lose 'em.
 

Reply to conservatory I & T in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
863
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
234
  • Question
Hi James. I agree that is a method of extending the ring which I have seen many times. However in this instance, the electrician who wired the...
Replies
11
Views
2K
  • Question
For anyone interested, I tested the supply side RCBO today and got a 1x I time of <130ms, so I don't believe it is a Type S. I did however have...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks