Piratepete
Hi Guys
No doubt this has been asked before, and the answer is already out there somewhere but I'm tired and the job is tomorrow so please bear with me.
Existing CU is back entry, spaced off the wall by an inch on a couple of vertical battens in a tight wooden cupboard. I'm intending the same mounting and cable entry arrangement
Back entry requirement is IP2XC which allows a gap of about 12mm od at each gland. It occurs to me that having gaps like this doesn't help if you're trying to keep an internal fire contained.
Is there any requirement to fill any gap between the cables and the edge of the quite large entry holes?
Cheers
Pete