Recently changed a consumer unit and had a problem with the upstairs lighting as it kept tripping rcd removed all lamps and checked all fittings , circuit tested out fine when insulation resistance r1+r2 and Zs but still kept tripping rcd so put circuit on non rcd side of consumer unit would I have to note this as deviation on the test sheet ? And add it in to the 'comments on existing installation ' section any ideas please ?
 
Recently changed a consumer unit and had a problem with the upstairs lighting as it kept tripping rcd removed all lamps and checked all fittings , circuit tested out fine when insulation resistance r1+r2 and Zs but still kept tripping rcd so put circuit on non rcd side of consumer unit would I have to note this as deviation on the test sheet ? And add it in to the 'comments on existing installation ' section any ideas please ?

No you should find and rectify the fault. Upstairs lights and downstairs lights on separate RCDs by any chance?
 
try a forum search on borrowed neutral. this is a classic case. landing light fed with L from downstairs cct.and N from upstairs cct.
 
Iam unable to rectify the fault as the property has been decorated and customer is unwilling to have fault rectified the circuit will have to stay on a Mcb now what are my options do I note it as a departure from bs7671 ?
 
what you have to do is put both lighting circuits onto the same RCD. preferably also on the same MCB.
 
Iam unable to rectify the fault as the property has been decorated and customer is unwilling to have fault rectified the circuit will have to stay on a Mcb now what are my options do I note it as a departure from bs7671 ?

You carry out testing for this before you start the job, not after you have finished it, and agree the fault finding and repair with the customer before starting. If they refuse to have it done then you walk away from the job.

If you leave the lighting circuit without RCD protection then the work you have done does not comply with the regulations, and makes a mockery of the point of installing a new CU. You have identified a potentially dangerous fault which could place the life of anyone working on the installation at risk, you now need to do something about this to make it safe.

If you have not made the customer aware of the possibility of finding such faults and the need to rectify them before starting then you may well have to carry out the repairs at your own cost.
 
I come across this one quite a lot. It's not ideal but if the customer really doesn't want the circuits segregated and you've already changed the board I'd put them both on one RCD and MCB as telectrix said. Not ideal but better than having one circuit not protected by an RCD.
 
I come across this one quite a lot. It's not ideal but if the customer really doesn't want the circuits segregated and you've already changed the board I'd put them both on one RCD and MCB as telectrix said. Not ideal but better than having one circuit not protected by an RCD.

Then it is your fault for changing the board without testing the installation properly beforehand, and you should be fixing it at your own expense.
 
I have this situation in my house.
Whoever installed experienced the same issues with tripping.
He did what Telectrix suggested.

I think I have a non destructive solution, can someone please critique ?
Put both circuits on the RCD side in separate MCBS

At the landing switch, wire it as a one way switch terminate cables.
Same with the hall swicth
Then fit a discreet flush mounted pir to operate the landing light. ?
 

Reply to Consumer unit change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
461
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

That's a hell of a big jump to make, an RCD trips therefore a rewire is required! If a wheel on your van gets a puncture do you go out and buy a...
Replies
6
Views
999
davesparks
D
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

  • Borrowed earth
    If mechanily protected would a 2.5 not suffice.you could manufacture metal conduit just to get...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
  • Duplicate posts
    Any suggestions for avoiding the duplicate posts that keep happening? I'm trying to delete mine...
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top