spud4dd

Hi, recently changed ccu from rewirable too modern dual rcd type. No probs with test results etc, only prob gas and water bonded with 6mm, wiring in old colours etc. But customer does not want walls ripping too bits too solve . Should i use EIC and put these items in (departures from bs7671) or PIR and give items the correct codes. thanks
 
Poking around the red book I find reg 131.8

Additions and alterations to an installation

No addition, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the RATING AND CONDITION of any EXISTING equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the addition or alteration, SHALL BE ADEQUATE.

It can also have implications for things like the dispensing with supp bonding in bathrooms which requires that the main bonding is fully up to scratch.

Have you got <0.05 ohms for each of them? not actually sure of the technical reasons for the BS7671 increase in bonding conductor size (has there been a rise in expected P.E.F.C.s?) but if they satisfy the 50 miliohm requirement why change them out.
 
Leave bonds as is, make a note in the deviations comment box on cert (not ideal but hey what can you do).

Supply customer with a letter/dissclaimer about undersized main equip bonds,
(could also give them a print off of the niceic bonding leaflet, they may say do it then ;))
You get customer to counter sign a copy of the letter & file it with the cert.

You have to issue an EIC, periodic is not the one to use for the installation of a cu.
 

Reply to Consumer Unit Change. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

That's a hell of a big jump to make, an RCD trips therefore a rewire is required! If a wheel on your van gets a puncture do you go out and buy a...
Replies
6
Views
956
davesparks
D
M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
2K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top