A Happy New Year to all!!
:clap: :clap: :clap:
:82: :82: :82: :82:

I have been asked what is the best thing to do in this situation: in a house there is a Consumer Unit a long way from the incoming supply. I believe the "tails" are 10mm cable, and go about 7-10m to reach the consumer unit. This is historic, the person now wants to rectify the situation. I suggest the easiest way is to put in 25mm tails of 2m length, to an overload protection device/switch fuse of 100A, then have the remainder of the run as the submain. I am not sure how to assess what size cable the submain should be. Any advise appreciated, especially as it is hard to find specifics on this particular problem.

THANKS!!!!
 
You really need to start by assessing the likely load. What is the rating of the existing final circuits and what sort of loads are they supplying?

Once you have this, you can sort out a suitable cable for your submain, possibly with some spare capacity for additional final circuits.
 
Thanks to Telectrix and Handysparks.
I can't assess the likely load, it is only advice that the chappie wants at the moment, and my info is limited - I would assume that it is no more of a load than an average 2 bedroom house, with only one occupant. The wiring is historic, I think he is after some grant work, so wants to make sure his wiring won't be condemned by the electrician. I will suggest to him the 25mm tails at 2m, then the switch fuse (is anything between 60 and 100A okay?) Then 16mm cable the rest of the way, which I will assume is 8m, to the CU.
Does this sound acceptable to your more experienced selves?
THANKS again!!
:):):)
 
If the main DNO cutout fuse is 100a, then I'd advise using an 80a fuse in your switch, if the DNO fuse is 80a, use a 60a. This allows for discrimination. But don't do anything until you've had a good look at the installation and taken into account the max load.

It's certainly not good to have the main cutout fuse protecting tails any longer than 3m.....if the DNO find out they'll send in a SWAT team. Not.
 
If the main DNO cutout fuse is 100a, then I'd advise using an 80a fuse in your switch, if the DNO fuse is 80a, use a 60a. This allows for discrimination. But don't do anything until you've had a good look at the installation and taken into account the max load.

It's certainly not good to have the main cutout fuse protecting tails any longer than 3m.....if the DNO find out they'll send in a SWAT team. Not.

There are some here that insist, .... The DNO, NICEIC, ELSCA, only require an isolator to be fitted on extended meter tails!! Now what an isolator is going to achieve, i don't know

Rather them than me!! lol!!
 

Reply to Consumer Unit, long meter tails, best plan of action in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
Issue is certain sizes of cable may theoretically be okay but upon the proper testing when it’s commissioned things like a thing may not test out...
Replies
8
Views
1K
  • Question
The norm is that it goes from the DSO (ESB) fuse to a DSO isolator with a contractor's side, and then to the main overcurrent device. The ESB...
Replies
9
Views
3K
In years gone by many of us would feed an additional small CU [say for a shower or outbuilding for example] with 6mm tails, often directly...
Replies
6
Views
2K
D
  • Question
The revised arrangement - please check that I have fully understood the points made in the above threads. Obviously a qualified electrician will...
Replies
5
Views
3K
Deleted member 155212
D
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
2K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks