Contactor advice | on ElectriciansForums
Guest viewing is limited
Discuss Contactor advice in the UK Electrical Forum area at ElectriciansForums.net
soulman
Durham
Hi all,
First of all i haven't much experience with contactors, I need to install a timer to switch 3 discharge lamps. I vaguely remember from my training that contactors should be used when using a timer unit to switch discharge lighting, as timer contacts will burn out when switching the load off.
My question is can i use the same circuit to switch the coil. L & N to timer input & top of contactor, link N to bottom of coil & SL to top of coil.
Salient question from Andy78; also the timer might not like the current surges of discharge lamps, but it would be a limited separation even if on another MCB.
[ElectriciansForums.net] Contactor advice[ElectriciansForums.net] Contactor advice
I knew you would be the guy with the diagrams Richard :smilewinkgrin:
@OP I know you can get timeclocks to handle small discharge loads, but the deciding factor might be cost. It may be cheaper to use a non discharge suitable timeclock and a contactor as per Richard's diagram.
Hi Richard on most of the timers i have looked at they are 8A resistive 8A inductive but all say no switching of discharge lighting or max 70w
Cheers
Sorry, I was not quite clear on that, I would use the contactor but I would expect that you could use a single 6A, maybe 10A MCB, maybe type C (depending on the number of fittings) to protect both the timer/contactor coil and the load. If you have to option to split the timer and contactor then why not, easier for fault finding.
Reply to Contactor advice in the UK Electrical Forum area at ElectriciansForums.net
I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...